Could you please send me a photo(s) which shows the current upstairs control wiring?
hmm odd the fpg images are not uploading tonight. I'll try again later
"The uploaded file was not an image as expected."
Discuss Changing original 32Amp contactors for solid state relays? in the Electric Underfloor Heating Wiring area at ElectriciansForums.net
Could you please send me a photo(s) which shows the current upstairs control wiring?
A standard DIN module is 17.5mm wide. So with two power meters that is 35mm - one for L1 and one for L2. Which leaves 220-35 = 185mm
A double pole 20A ABB contactor is a standard DIN module -the spec says 18mm. So you could fit in up to 10 of them.
ABB ESB20-20N-01 - https://new.abb.com/products/1SBE121111R0120/esb20-20n-01-installation-contactor
Could you have a think about how you want the zones arranged knowing that you have room for circa 12 standard DIN modules - and do you want a power meter for each zone?
The 4 pole sounds fine. If you send me its details I will give it the once over.
I cannot read the make - what is it?
At first blush they look rather cheap and cheerful. Here is a proposal: I will send you some ABB silent relays and perhaps you will make a donation to a children's charity in Uruguay akin to the UK's NSPCC - what say you?
The seller of Steck has confirmed they are quiet and do not emit the same noise as the conventional contactors.
Thanks will do.Remember to switch off all the electricity and check everything is dead before you work on the swap. Label up the wiring too so the pairs are identifiable and recorded somehow near the contactor. Last, all connections must be tight and use all the strands of the conductors without any of them showing outside the entry to the terminal channel. Then it will nearly be as good a job as done by DPG ( ) - but only nearly so don't get carried away. Let us know how you get on - pictures are always good if you want your work checked and assessed.
The UFH heating is cleverly connected across L1, L2 and N as shown in the diagram below. The black bar above the 5 cbs confused me; the voltage measurements clarified the situation.
Sometime please tell me L1 to L2 voltage. I am pretty sure you have a 3 phase supply arranged as I have drawn.
Otherwise I would swap the contactors for silent ones. Solid state switches can fail short-circuit which would not be a good thing so don't fit them. They also need substantial heatsinks and ventilation around these because they would get too hot without. If it was me I'd buy silent contactors. The three sets of UFH are each protected by a 20A cb. A 32A contactor is beefy enough to carry up to 20A 'all day long' and be more reliable than one rated close to 20A. Space the power meters and contactors apart so that there is some air movement and one does not warm the other.
Thank you for your patience!
Marconi
In order to measure the power consumed by each of the three UFH zones the power meters P need to wired in between the zones and the contactor C as I have drawn in my attached diagram.
The same holds for elsewhere in your home to monitor power consumption by each UFH zone. So you should revisit how the power meters have been wired in - I cannot do that for you because I can no longer open any attached images in previous posts.
The total power consumption of your home however is measured by two meters - you might have thought three were required. For a three phase three wire system only two meters are necessary; the total power consumption being the sum of the two readings. Blondel's theorem if you want to look it up. My second attachment shows how they are connected. Note how the two meters are both connected to the third line N/L3.
If there were three meters they would be connected as in the last drawing, one in each line and the meters then connected to a common star node. Simply by making one of the lines common to the power meters one of the three meters becomes superfluous and an economy can be made.
Blondel's theorem:
Blondel’s theorem | Power in Poly-Phase System | Electricalvoice - https://electricalvoice.com/blondels-theorem-power-in-poly-phase-system/
Sorry just posted and saw your post above as I'm reading through it now.
Perfect many thanks again.
I'll go for set up #2. 2 power meters between the CBS and contactor. Just need the total for all.
So my figures for the UFH#1/#2 are incorrect as I do not have L2 connected even though the PM shows some power feeding through it, possibly just a % of the total power. Did suspect the street side new meter was reading more KwH than I calculated when running the UFH upstairs. Downstairs is pretty much spot on.
Will purchase another PM.
[automerge]1595451726[/automerge]
I have found these specs (mine is the 40 amp version).
Model Number:
DM25S
Display Type:
Digital Only
Phase:
Single Phase
Measuring Energy Range:
0-99999
Accuracy Class:
Class1
Output Voltage:
220VAC,110VAC
Operating Temperature:
-25℃~+55℃
Dimensions:
DIN EN50022 Standard
Product Name:
Meter Energy
Width:
18mm (One Module)
Current Specification (A):
5(20),5(30)A,5(40)A
Frequency:
50-60HZ
Constant:
2000imp/kWh
Display Mode:
5+1 Digits Counter Display
Connection Mode:
Direct Mode
Standard:
IEC60253-21
Yours will work but it is simpler to do it like my attached diagram. Add the wire I have indicated in blue to go to the link between the middle terminals of the CTR and remove the two I have indicated in white.
(A power meter needs to know the voltage which it obtains from the two inputs and the current flow between the line input and line output. This why we can dispense with the white wires.)
Many thanks Marconi.
I think I will do the same with the downstairs wiring. 2 x powermeters between the main CBS and contactors (currently have 3 after the 3 contactors). I really only need to measure the total going through the 3 phase wiring now. This way I can re-use one of the 3 PM's I have and install it upstairs. So I'll have 2 downstairs and 2 upstairs. Makes the wiring a bit neater also.
Have a good weekend