I have been doing some subbying work for an NICEIC approved sparks. He will channel out the plaster of ceilings to run new cables in.
For example, today there was on light in a ceiling in an corridor and we were removing this and replacing with 4 spotlights. So the spark said to take out the plaster under the joists and lay the cable in. I wasnt happy about this but its his job and his name on the cert.
I suggested that this wasnt a good idea and shouldnt be done. He said find me a reg to say you cant do it. So I have looked in the BYB, in particular 522.6.201 to 522.6.204. As the joists are not being notched or drilled there is no problem there. 522.6.202 and 522.6.203 are refering to cables buried in walls.
This leaves 522.6.201
the first line is in regard to the cable being run in such a position that it wont be damaged by contact with the floor or ceilings or fixings. This seems to me to be the only reg that outlaws the channeling of the ceiling. But if the ceiling is already installed the fixings wont damage the new cable.
I still think its bad practice to channel the ceilings but am getting a bit lost as to whether the regs allow it
For example, today there was on light in a ceiling in an corridor and we were removing this and replacing with 4 spotlights. So the spark said to take out the plaster under the joists and lay the cable in. I wasnt happy about this but its his job and his name on the cert.
I suggested that this wasnt a good idea and shouldnt be done. He said find me a reg to say you cant do it. So I have looked in the BYB, in particular 522.6.201 to 522.6.204. As the joists are not being notched or drilled there is no problem there. 522.6.202 and 522.6.203 are refering to cables buried in walls.
This leaves 522.6.201
the first line is in regard to the cable being run in such a position that it wont be damaged by contact with the floor or ceilings or fixings. This seems to me to be the only reg that outlaws the channeling of the ceiling. But if the ceiling is already installed the fixings wont damage the new cable.
I still think its bad practice to channel the ceilings but am getting a bit lost as to whether the regs allow it