I have one of these and it does the job well:
If you don't need continuity testing then this is the daddy of them all:Martindale VT12 Voltage and Continuity Tester
Martindale VT12 Voltage & Continuity Tester - MARVT12 The Brand New Martindale VT12 is an excellent value Voltage and Continuity tester for universal applications. The VT12 is constructed in accordance with the latest safety standards and guarantees safe and reliable measurements and...www.test-meter.co.uk
But equally you get cheap voltage-only testers such as this from the DIY houses:Drummond MTL20 Test Lamp
John Drummond Test Lamp MTL20 The John Drummond MTL20 Test Lamp gives safe indication of voltage between 50V and 500V AC/DC. The MTL20 test lamp housing and probe both have a finger shield and insulated probe tip with only 4mm of exposed metal. A two layer double insulated cable with white...www.test-meter.co.uk
All testers should be "proved" before and after use by testing on a known voltage source to check they are really working. Some models claim to be self-proving, and to some extend the likes of the Martindale tester (above) will let you know something is working just by checking it bleeps on continuity, but as a professional then something like this is worth considering:TIS Voltage Tester
• Voltage range 12V to 690V • Automatic polarity indication • One hand operation for testing sockets• Compact pocket size design• Probe tip protection• No batteries required• Extra bright LEDs• Does not trip RCDswww.toolstation.com
Otherwise you really must check the tester on a known live supply first, and obviously that is a dangerous step to take compared to a limited-energy battery unit designed for testing.4299 Proving Unit
Intelligent voltage ramp testing for voltage indicators and multimeterswww.cef.co.uk
OK.Oh nice brilliant thank you so much for yhat I'll have a quick look at them now.
It is not the same thing. The usual "voltage tester" takes a mA or two to drive the LEDs and that allows it to check there is a real power supply there, and not a few uA of current from capacitive coupling (AKA "phantom voltage").My dad just gave me this as he just found it jn his cupbard he bought years ago.. Seems like this is different as voltage check goes only up to 600v.
Is that correct?
Looking on the interweb there are ad's everywhere for it! And youtube vids!My dad just gave me this as he just found it jn his cupbard he bought years ago.. Seems like this is different as voltage check goes only up to 600v.
Looking on the interweb there are ad's everywhere for it! And youtube vids!
It does seem to be a 'proper' cat III multimeter, but with an input impedance of 10Meg, so it will suffer from the 'ghost voltage' syndrome mentioned above.
While the voltage ranges go up to 600v, the DC and AC current ranges are limited to mV and mA, so it seems more suited to electronics work.
So all in all good for experimenting on battery and low voltage things, but not for mains work, especially dead testing.
I think you've had some excellent answers already. My 2 cents is that a 2 pole tester is a great (if not essential) investment and the TIS unit above does the job well. For proving dead, and basic continuity or no continuity it's fine.
Being able to measure very small resistances accurately and perform insulation resistance test is the next step, and assuming you aren't ready to shell out for a multifunction tester, then keep a look out for the Megger BM series, that can do 250 and 500v insulation tests and continuity tests to an accuracy of 0.01 ohms. They come up on ebay quite a lot and are fantastic little testers.
Also keep an eye out for Megger 15xx series multi-function testers that are still in calibration, occasionally these come up for silly money as they are getting a bit old now, but they are extremely well made (better than the 17xx series IMHO) and do the job.
Hope that helps.
You need either a MFT or a simple 'Megger MIT230' style of IR tester that gives you low resistance measurements at enough current to show poor joints, etc. If on a budget then a 2nd hand one might be found for £100 or so.To do ab R1+R2 testing, continuity, resistance testing would I need a multifunction tester or can I do it on a simple 2 pole voltage tester?
For professional work you would be expected to have it calibrated once per year, cost varies but CEF do "calibration days" where you hand it in and it is about £30 per item.Also how often do they need collaborating ? Is it expensive ? And is is it mandatory?
You need either a MFT or a simple 'Megger MIT230' style of IR tester that gives you low resistance measurements at enough current to show poor joints, etc. If on a budget then a 2nd hand one might be found for £100 or so.
Or new on a budget, something like this:
Test Meter PRO TMP600 Electrical Insulation Tester
#html-body [data-pb-style=RKRH7Q9]{justify-content:flex-start;display:flex;flex-direction:column;background-position:left top;background-size:cover;background-repeat:no-repeat;background-attachment:scroll;border-style:none;border-width:1px;border-radius:0;margin:0 0 10px;padding:10px}#html-body...www.test-meter.co.uk
For professional work you would be expected to have it calibrated once per year, cost varies but CEF do "calibration days" where you hand it in and it is about £30 per item.
In between, and if on budget/hobby, then the CalCard gives you a very good indication for IR and continuity testing:
However, that won't check other aspects of a MFT, like RCD testing, Zs measurement, etc. But in most cases modern meters are either working or very broken, so the calcard would show something up. Probably in over half of the cases of dodgy measurements the test leads are to blame, so a spare set is worth getting if you suspect the meter is unreliable before damning it.
Hi mate thanks for that great advice
To do ab R1+R2 testing, continuity, resistance testing would I need a multifunction tester or can I do it on a simple 2 pole voltage tester?
Also how often do they need collaborating ? Is it expensive ? And is is it mandatory?
The new unit that @pc1966 suggested would be fine for Insulation Resistance (IR) tests, which is basically "pressure testing" cables. I'm actually having slight doubts it is also intended to be an accurate continuity tester, i.e. that it can measure resistances to the nearest 0.01 ohms. I looked and couldn't see the range/accuracy information, so I could be wrong.So the new one you just posted a link to . TMT one. Could that be used in a professional capacity in the future once I've done college In a couple of years. Or does it not meet the standard and lacks capability ?
There's a RS version of that meter. I have one in my hand right now. Actually I have 4 of them but thats another story! I can't get my phone to post a link to the RS site but if you go to RS web site and do a search for 123-1931 it'll give you all the info. £165 at RS. They are also sold under the Tenma and Amecal brands.I can't see detailed specifications for the"Test Meter PRO TMP600" either, but the headline values look OK. Might be worth asking for them.
Good info Moley, that confirms that on 40 ohm range it gives 0.01 +-1.2% + 3, so it would be fine.
All comes down to money, like most things!
Yep, it looks good, and for an extra fee you can buy calibration with it.Thanks so much for your detailed responses
So based on this is the TMP tester also good to go? For resistance and continuity.
If you don't mind a 2nd hand unit I've got the RS model I could sell. I'm on my laptop so hopefully I can post the link to the RS site HERE There's no leads or case with it though.
The new unit that @pc1966 suggested would be fine for Insulation Resistance (IR) tests, which is basically "pressure testing" cables. I'm actually having slight doubts it is also intended to be an accurate continuity tester, i.e. that it can measure resistances to the nearest 0.01 ohms. I looked and couldn't see the range/accuracy information, so I could be wrong.
If on a budget then the most bang for your buck is probably a Megger BM or MIT, which can be calibrated and used professionally. Either would be fine.
Ebay is full of units like this:
Megger Mit230 Insulation and Continuity Tester for sale online | eBay
Find many great new & used options and get the best deals for Megger Mit230 Insulation and Continuity Tester at the best online prices at eBay! Free delivery for many products!www.ebay.co.uk
Megger BM223 Insulation And Continuity Tester | eBay
Find many great new & used options and get the best deals for Megger BM223 Insulation And Continuity Tester at the best online prices at eBay! Free delivery for many products.www.ebay.co.uk
You'd need a set of test leads with the 2nd one.
Either of those gives you 50% of what you need for professional testing.
You could later add a loop tester and RCD tester, or a unit that does both. But it is likely you will want the convenience of an all-in-one multifunction tester that does all the tests: insulation resistance, continuity, earth loop impedance tests, and RCD tests. (at a minimum).
(Even if you do plan to get an MFT one day, having a 2nd IR tester is very useful when fault finding, so getting a continuity and IR tester is still a good investment IMHO)
Hi mate
I Managed to buy the 2nd one....where can I buy the leads from ? Or which one should I look for ?
Standard 4mm plug test leads. GS38 tips.
Something like this would be fine. Kewtech Test Leads 1.03m - Screwfix - https://www.NoLinkingToThis/p/kewtech-test-leads-1-03m/28760
There will be cheaper on ebay.
The thing about those is that you will want to switch between probes and clips. Clips are more generally useful for the testing we are talking about. I think those leads are permanently probes.UKstock Test leads multimeter 10A 1000V 35” lead 4mm banana plug Fine Tip Probes | eBay
<p>UK post only Test leads multimeter 10Amp 1000volt 35” lead. </p><p>Note pictures taken were by ourselves with SMD needle point probes, an economical quality set of test leads for fine work 👍 </p><br /><p>With 4 mm banana plug fittings, Black and Red needle point probe.. buy from an eBay...www.ebay.co.uk
Would that be suffice?
As I'm not professional yet got a couple of years left I'm college. Would they do for home use?
Reply to Cheap Voltage and continuity tester? in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.