J

jagslaglil

Hi all,
does anyone know if when running circuits in conduit , whether running a socket circuit and a lighting circuit together ,
is acceptable when passing through the light fittings ( fluorescent)
i personally think it is not as 2 circuits need to be isolated to replace each light and the socket wires would have to be cut and rejoined !!

cheers
Jagslaglil
 
if i read it right, you're visualising the conduit entering the florry at on end and out the other, with a socket circuit passing through the fitting. if that's so, then it's a big NO. however, if the conduit passes over the florry and the lighting cables come out through a conduit box into the fitting, then it's OK.
 
You are correct,thanks. I have been preaching this for years ! The light fittings are being installed in lift shafts ,vertically,with the conduit entering the top and exiting the bottom. Along with the wiring connecting to the fittings are strappers going to a switch in the pit ( same circuit ) plus a radial socket circuit ( separate CCT ) passing thru all the lights to the pit !
I have been asked to find something in writing to prove this is wrong !
cheers
Jag
 
You shouldn't even be running the lighting circuit through the lighting fitting let alone the socket circuit!! Who the hell designed this installation method. Apart from anything else the fitting is not deemed as a wireway containment system!! What happens when one of these fittings get's damaged or goes U/S and need replacing?? Light fittings should be tee'd off the conduit raceway not become part of the raceway....
 
Thanks for the replies chaps !
i know it shouldn't be done and practise what I preach ,but a lot of people in the lift industry are doing it this way ! Also a lot of the time it is steel conduit passing in and out of a plastic/fibre light base !
and therefore the conduits between the fittings are not earthed !!!
I was just hoping to find something with a ref. no. to help clarify my points

cheers
Jag
 
Imagine the nightmare situation for the poor spark attending site to replace a faulty light though with a ring main running through it, a nightmare and a costly job. I would alter the conduit and stick 2 through boxes at 600mm2 centre to centre apart in the run and sit the fluorescent on that myself, do it now and do it right.
 
You could use Reg 522.2.100 for a start but this only cover heat damage to cable (in this case it would be the cables running close to the ballast , there may be something in a best practice guide i will keep looking
 
Yes, I agree thank you . My biggest argument against is the fact that a lot of the time they are using galv. Conduit and it is isolated from the earthing system by each light fitting !!!
Thanks for replying
Jag
 
Seems really silly to install it that way.
BS7671 section 528.3.5 states "No cable shall be run in a lift or hoist shaft unless it forms part of the lift installation as defined in BS EN 81-1 series.
I take it you have had a look at BS EN 81-1.
 
Seems really silly to install it that way.
BS7671 section 528.3.5 states "No cable shall be run in a lift or hoist shaft unless it forms part of the lift installation as defined in BS EN 81-1 series.
I take it you have had a look at BS EN 81-1.

Lights and sockets are part of the Lift installation, it'd be dark in the shaft without lights..
 

Reply to Circuit segregation ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
488
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
620
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
660
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock