yes....unless you need to use RCD for fault protection on a TT system and it's not feeding a socket outlet requiring RCD.
 
so does the socket need to be rcd protected, even if the cable does not?
 
Who's using the socket, what's its purpose location etc. For a new socket I would recommend RCD for sure regardless of if technically you "can get away without"
 
where does KFH come from? i assume it's not Kentucky Fried Hedgehog. :lol:
 
Ways to do it...
1) RCBO in consumer unit (unless cu doesn't accept them)
2) RCD in enclosure next to cu in-line with hallway RFC
3) RCD socket (many don't look ugly at all these days

Personally, I wouldn't install a socket outlet without RCD protection.
 
Code:
They don't really look ugly. Just a green and a red/blue switch instead of 2 white ones. As guitarist say though. I wouldn't even think about putting in a socket without RCD protection these days unless is was specifies or for special equipment (server, it equipment etc) also if its clipped direct does that mean no mechanical protection?
 
If this comes up again, 411.3.3 is the relevant Reg.
Basically,almost all socket outlets in domestic premises need to be RCD protected, unless they are only for the use of one particular appliance.
 
Listening to some here, it makes you wonder how we oldies all managed to stay alive without all these RCD devices being available in the past!!
 
Listening to some here, it makes you wonder how we oldies all managed to stay alive without all these RCD devices being available in the past!!

Back in the olden days, there was something called "workmanship". Judging by some of the jobs I see these so-called "electricians" do, it's a damn good job that we do have RCD's.
 
BUT JUST FITTING AN rcd TO ALMOST EVERYTHING IS ALL PART OF THE DUMBING DOWN.. SOD THE zS ETC, THE RCD WILL FIX IT.
 
I've seen high Zs's for RFC on fairly new installs but only because a type C RCBO was used ,if a type B had be used then the Zs would be satisfactory .So would there be any reason to change the RCBO to a type B so that the circuit is within the maximum earth loop? . I've never sited this as a deviation on a EICR as the disconnection time is achieved by the RCBO although I feel its an over site in the design stages.
 
Indeed mate. We've had a few posts like that recently...."the Zs is really high on this TN system, but it's ok because it has an RCD...."
Argh I hate it when they say that all very well unless the /RCD fails I aways try and design the install so it gets the lowest Zs possible Regardless of an RCD , E54 I remember when I was a kid sticking my toe on the bars of an electric fire kept getting a tingle kept doing it , it was a very old VIR install single fuses in little wooden boxes wasn't till I did an inspection on the house 40 years later that I found the polarity was the wrong way round so I was zapping myself lol no wonder my hair looks like a monks
 
makes me wonder then if the polarity had been the right way round, you might have got more than a tingle.
 
OP question Am I right in thinking a new circuit clipped on the surface doesn't require rcd protection ?

I thought only if you could see the whole length of the cable clipped to the surface from A to B. If cable went through wall to another room /location then rcd required.
 
OP question Am I right in thinking a new circuit clipped on the surface doesn't require rcd protection ?

I thought only if you could see the whole length of the cable clipped to the surface from A to B. If cable went through wall to another room /location then rcd required.


That's what you think?
 
It is only required for cables that are buried in the walls and may be nailed into or such, not for cables passing through a wall as they cannot readily be damaged.

Or for those socket outlets intended to supply outdoor equipment, regardless of installation method.

Richard, I was hoping driverman would read through the regs and give us his opinions. :)
 
I've seen high Zs's for RFC on fairly new installs but only because a type C RCBO was used ,if a type B had be used then the Zs would be satisfactory .So would there be any reason to change the RCBO to a type B so that the circuit is within the maximum earth loop? . I've never sited this as a deviation on a EICR as the disconnection time is achieved by the RCBO although I feel its an over site in the design stages.

Could be a type C for a reason? Also if you do change it to a type B as with all breakers make sure its in the permissable maximum values if the circuit is tested cold and dont just go off the table in the regs.

And yes i would change it to a type B from a C to bring it into the permitted Zs.

im not sure if iv understood the post correctly with this reply to be honest haha so apologies if this seems a little arsey.
 
The circuits in question were for feeding 6 socket on a RF in school classroom for general use only 1 computer and a white board so could not see a reason for the C type . It was an EICR that identified this so maybe I should of sited it as a code 3. I have noticed that in general Merlin Gerin RCBOs are type C
 

Reply to Clipped surface in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
617
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
510
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
360
This might come across as a really daft question to people who work with cable tray quite often but as part of my AM2, I am to clip FP200 to the...
Replies
31
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
895

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock