Discuss Combi boiler with dual heating zones and 2x programmable stats. in the Central Heating Systems area at ElectriciansForums.net

G

GreasyWookie

First post so let me start by saying hello to all!

I'm a plumber not an electrician, nor do I consider myself a heating engineer and would appreciate any help...

What I have is a Worchester combination boiler which is currently hooked up to a Honeywell programmable room stat. We have installed UFH in a newly built extension and the client wants independent zone control so he can have the UFH come on before the rest of the heating. I have installed 2x 2 port zone valves each with its own RF digital 7 day programmable thermostat but I'm having trouble getting my head around the wiring. So far I've added a Drayton wiring center hooked up the wires for the zone valves and room stats as per a standard s-plan system but with the UFH in place of DHW, I presume having programmable stats means I don't need a 2 channel programmer? If this is the case, what do I do with the brown wires coming from the zone valves that normally go to the programmer, are they now redundant or do I need to connect them to the programmable stats? After several hours looking at various wiring diagrams and repeatedly banging my head against the desk I'm none the wiser.

Please Help!

Many thanks.
 
If this is the case, what do I do with the brown wires coming from the zone valves that normally go to the programmer,

Sorry, brainfart... the browns are linked to the call for heat from the stats. It's the commons for the two stats that normally go to the programmer that are the ones causing my issue.
 
Commons for the stats would be connected to a permanent live in this case as the stat is doing the job of both the programmer and the stat in a normal system.
In a programmer this link is often made internally, though will occasionally require a physical wire link to be fitted.
 
Thanks for the replies, that definitely helps, just one small point, the instructions for the zone valves (which are Honeywell btw) show the greys as permanent live and the oranges going to the boiler, so I would guess I do as Leesparkykent says but substitute the grey for orange?
 
the instructions for the zone valves (which are Honeywell btw) show the greys as permanent live and the oranges going to the boiler

Update...

It's working... mostly. So today I took the info you guys gave me, binned the old programmer, wired in the two new ones with both commons and the zone valve orange wires going to the boilers Ls terminal, both the call linked to the zone valve browns and back to the boilers Lr terminal and hey presto! So now I can ramp up the temp on either of the stats, the corresponding zone valve opens boiler fires and everything is tickety boo right? Not quite... when the UFH pump clicks in the main breaker trips and we lose all power. We're using Polypipe UFH with a 2/3 circuit ZRU, I've installed these before with system boilers in s-plan plus config without any issues, I tried wiring the ZRU to the permanent live from the spur and the brown on the UFH zone valve (a suggestion I found in another thread on this forum) both had the same result - boiler fires runs for a few mins until the UFH pump clicks in (the ZRU prevents this until the water temp reaches 45 degrees) then the breaker trips off. If I disconnect the UFH pump and allow it to run the CH only it works perfectly. I'm stumped.

Any ideas, anyone?

PS. It just occurred to me I should have tried swapping the oranges and greys from the zone valves so it's wired as Leesparkykent says

commons for the stats and the greys of the valves should be connected to the LS terminal of the boiler.

Could this be my issue? If so, why is it working without the UFH pump in play?
 
Where you taking power from for that ZRU? It needs to be on the same supply as the boiler 3amp Fused Spur.

What you doing with the Neutral when your swapping the brown onto the Ls & brown of ZV?
 
Not sure my friend, obviously something is a miss, my guess is the neutral wrong somewhere, maybe in the pump if you wired it, or somewhere else on that ZRU.

Let me know the outcome i would be interested.
 
Thanks for the replies, that definitely helps, just one small point, the instructions for the zone valves (which are Honeywell btw) show the greys as permanent live and the oranges going to the boiler, so I would guess I do as Leesparkykent says but substitute the grey for orange?

No, the Ls terminal of the Worcester boiler is the live feed to the external controls, so the grey from the valve connects back to that, the orange of the valve connects back to the Lr terminal of the boiler.

Reading your other posts it sounds a bit like you've connected your external controls to the live from the switched spur instead of to the Ls terminal? Unless it is an Ri which does not have this terminal then it's not in accordance with manufacturers instructions and they could refuse a warranty claim based on this.
 
Where you taking power from for that ZRU? It needs to be on the same supply as the boiler 3amp Fused Spur.

What you doing with the Neutral when your swapping the brown onto the Ls & brown of ZV?

On a Worcester, and some other boilers the external controls need to be connected to the live out from the boiler and not to the switched spur directly.
 
Update...

It's working... mostly. So today I took the info you guys gave me, binned the old programmer, wired in the two new ones with both commons and the zone valve orange wires going to the boilers Ls terminal, both the call linked to the zone valve browns and back to the boilers Lr terminal and hey presto! So now I can ramp up the temp on either of the stats, the corresponding zone valve opens boiler fires and everything is tickety boo right? Not quite... when the UFH pump clicks in the main breaker trips and we lose all power. We're using Polypipe UFH with a 2/3 circuit ZRU, I've installed these before with system boilers in s-plan plus config without any issues, I tried wiring the ZRU to the permanent live from the spur and the brown on the UFH zone valve (a suggestion I found in another thread on this forum) both had the same result - boiler fires runs for a few mins until the UFH pump clicks in (the ZRU prevents this until the water temp reaches 45 degrees) then the breaker trips off. If I disconnect the UFH pump and allow it to run the CH only it works perfectly. I'm stumped.

Any ideas, anyone?

PS. It just occurred to me I should have tried swapping the oranges and greys from the zone valves so it's wired as Leesparkykent says



Could this be my issue? If so, why is it working without the UFH pump in play?

Orange and grey are just either side of the microswitch so will work either way round, but the normally accepted way is to use grey as the switch common and orange as the switched live out.

Can you confirm that the underfloor heating and the boiler are all fed via the one switched fused spur? It sounds like you might have two diffent circuit sports linked together here, which is a very dangerous situation so be very careful until you have confirmed this!
 
LS is a live supply from the boiler to your external controls. LR is a live return to the boiler from your external controls.

No, the Ls terminal of the Worcester boiler is the live feed to the external controls, so the grey from the valve connects back to that, the orange of the valve connects back to the Lr terminal of the boiler.

Can you confirm that the underfloor heating and the boiler are all fed via the one switched fused spur? It sounds like you might have two diffent circuit sports linked together here, which is a very dangerous situation so be very careful until you have confirmed this!

Yes they're both on the same spur. The spur feeds a drayton wiring centre and everything is connected to that.

I think I might understand what's happening now. If the stat commons and ZV greys should be receiving power from LS then The ZRU needs to receive power from there too and only the boiler live connected directly to the spur. The the stats call for heat and ZV orange back to Lr to complete the circuit? I think I effectively had the ZRU live connected to a neutral. I'll be back there tomorrow to try and solve this so I'll let you know how it goes.
 
Found the problem, the drayton wiring center had a factory fitted link from the live on the spur to the same terminal that I had the boiler LS connected to, so the two lives were crossed. Removed the link, wired the ZV greys & stat commons to the LS, ZV orange to LR, the stats call for heat to ZV brown and ZRU + boiler direct to the spur and its all working perfectly.

Many thanks for all the input, not only did it help solve this problem but I learned a few things about what each wire actually does so I'll no longer be blindly following the wiring diagram... as I discovered not all systems are wired the same and the diagrams are not always 100% accurate.
 

Reply to Combi boiler with dual heating zones and 2x programmable stats. in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
380
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
618
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
834
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
941

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock