hi,

Recently done the 2019 Compex , the Velcro equipment board is an online assessment now with drop down menus and I failed the Ex01 part of this, is there anyone who can clarify the following for my knowledge please

Exd equipment can be used in zone 1 and 2 also
If I have a cable 3m long direct entry, IIC Gas group with any internal volume Exd box I use a barrier gland? , if the cable entry is more than 6mm thread I don't need an IP washer?

any help appredciated
 
Barrier gland is not required for Exe box. Exe by its very nature and design shall not contain sources of ignition. Barrier gland is required in this instance only for the light switch which must be Exd. IIc gas means you need the barrier only on the light switch in this case.

6mm thread will satisfy the minimum IP54 rating for Exe, but if the JB has a higher rating then you need to fit an IP washer to maintain the higher IP rating.

Metal JB with 6 threads - your CPC can double as earth. If it is non-metal and has an internal earthing plate then you need a lock ring, maybe a serrated washer. Non metal with no earthing plate then you need a banjo and IP.

Basically choose the JB or fitting to the gas group, the T class and the IP rating and then build each item up from there one by one.

Compex is based on minimum standards, as such your barrier gland will be a fail on Exe. Rule of thumb is use Universal gland for everything, barrier only where it is needed. Where a stuffing gland is needed then it must match the classification of the JB and the IP rating (dual Exe / Exd if it’s there).

What they used to tell you on the 5 day was to fit an IP to everything as it was not a fail, although it is a demerit on the refresher and could contribute to a fail!

Ps - I am basing this on the Velcro board refresher, 2018, if it has been changed since I know not.
 
hi,

thanks for the reply, could you help me clarify the following please regarding Exd and barrier glands,

IIC Gas any internal volume Exd equipment needs a barrier yes
IIB and IIA greater than 2 litres needs a barrier
IIB and IIA less than 2 litres not required

Exde equipment does not need a barrier
What does the 3m cable rule mean

any help appreciated thanks
gazmon
 
Based on the latest EEMUA toolbox guide your statements are correct.

The reason that Exde does not need a barrier is that the main protection of the equipment is Exd, but the cable entry is Exe. Basically you generally have a seperate Exe entry for the cables, using Exe terminals for the cable connections, which is sealed from the main part of the equipment which is Exd. Exe can not have sparking components, so negates the need for a barrier gland.

3 metre cable rule means that if the cable is >3m then you can use a standard Exd gland. <3m you need to use a barrier (IIa or IIb). IIc will need a barrier gland no matter what.

Refer pages 42, 43 on the toolbox guide for Exd gland selection.
 
Thanks again for your info

Your reply refers solely to use of Exd quipment regarding barriers etc yes?

I’m thinking from memory that I had a 3m cable feeding a switch , can you remember if there was a requirement or situation presented where you had to use a barrier gland ? If I had a Exde switch I could eliminate the barrier yes

Just thinking here , it’s minimum standard
 
If the area is IIc and the equipment Exd, yes you need a barrier gland. If the cable is less than 3m in a IIa or or IIb zone then an Exd gland is NOT suitable. It has to be a barrier. Likewise if the volume on Exd is >2 litres you need a barrier.

The principle of Exde is that the cable termination is Exe whist the main protection of the equipment is Exd so a barrier is not required.
 

Reply to Compex Units course help and advice please in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all, I have a CompEx 01 re-sit this week. I have passed the full course once before and I have received no feedback as to why I have failed the...
Replies
1
Views
1K
Hi all, ive found myself in a bit of a desperate situation here. I sat my compex 10 months ago and failed sections 01 and 04. I was meant to...
Replies
1
Views
9K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock