OP
Deleted member 26818
Do you have to prove anything?
Who are you proving to?
How does entering calculated values you know are likely to be inaccurate on a schedule of test results prove anything?
Personally, if there were a reason why I could not conduct a Zs test, I would calculate the result and if the value was such that ADS would not be achieved, I would either then conduct the Zs test or state further investigation is required.
I would not enter the calculated value as a test result and run the risk that someone else might actually conduct the test proving my value to be incorrect.
Who are you proving to?
How does entering calculated values you know are likely to be inaccurate on a schedule of test results prove anything?
Personally, if there were a reason why I could not conduct a Zs test, I would calculate the result and if the value was such that ADS would not be achieved, I would either then conduct the Zs test or state further investigation is required.
I would not enter the calculated value as a test result and run the risk that someone else might actually conduct the test proving my value to be incorrect.