Discuss Condition report for the old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

Radius

I have to do a Condition Report for an old installation. Everything is ok but the installation doesn't have RCD's, even for those circuits required by the 17th Edition. Can I write that the installation is "satisfactory" without RCD's ?
 
any socket outlets with the potential to be used outside or circuits entering a bathroom where satisfactory supplementary bonding is not present would warrant a c2- making the EICR unsatisfactory.
 
any socket outlets with the potential to be used outside or circuits entering a bathroom where satisfactory supplementary bonding is not present would warrant a c2- making the EICR unsatisfactory.

Not that I do EICR's.. but if OP's installation done to correct regs at the time, surly that will be OK. Would not just a C3 suffice?
 
Yes quite right, if every house in the country without a modern DB board considered a C2, everyone would have to move out to hotels due to the extreme danger of being in the house pmsl.
 

Reply to Condition report for the old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Replies
7
Views
887
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
NICEIC Certification Scheme SPD on old consumer unit?
Under amendment 2 of the BS7671, there is now a requirement to fit an SPD as standard. I am due to install a new outdoor socket circuit on an...
Replies
2
Views
2K
4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall. Current carrying...
Replies
6
Views
935

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock