Discuss Condition Reporting on static caravan site customer wants only 10% testing ????? in the The Welcome Forum area at ElectriciansForums.net

P

pmasouthwestltd

Hi

I have started testing on a large caravan site i did a condition report and full inspection and testing on one caravan took me 3 hours.

The previous contractor (Niceic domestic installer ) does 10 caravans total of two people in 4-5 hours including certificates

My client has now asked me to do a condition report only 10% to be tested as thats what previous contractor did, can this be done on limitations/extent to be agreed???


Personally i like every thing 100% and i don't like a bodge job i rather walk away please help!!!

NICEIC has said that the company/ person should be an approve contractor as it is commercial. (im approved contractor)

But they did say that any one does not have to be registered and could use the BS7671 template or purchase the green forms. If any thing when wrong then trading standard would be involed



Thanks

Pete
 
If that is what the customer wants then do that, just mention that the 10% should be sequenced and the testing frequency should be increased 10 fold to cover the whole caravan in the required time!

If everything seems to be OK then you could do a 10% limitation, but it is becoming a bit pointless doing the inspection.
3 hours seems a little high for 1 caravan, but I do not know the level of equipment present and access and information so I could be wrong.
 
If that is what the customer wants then do that, just mention that the 10% should be sequenced and the testing frequency should be increased 10 fold to cover the whole caravan in the required time!

If everything seems to be OK then you could do a 10% limitation, but it is becoming a bit pointless doing the inspection.
3 hours seems a little high for 1 caravan, but I do not know the level of equipment present and access and information so I could be wrong.

So I do number of points take the install sort ready for ring circuit the. R2 + Insulation resistance on all cubic units they have 30 spot lights 3 fans and 10 double socket with 3 electrical app :) then I do zs both cu at caravan and hook up with pfc then rcd hook up and cu

30 mins form filling

am i doing to much lol
 
Your post does not seem to make a lot of sense but I think you are about right on the testing. The units are larger than I had anticipated. Downlights are a nuisance. 30 mins form filing is quick for me.
 
a lot of sites do percentage tests, say a different 10% every few months till the lot has been tested

at the end of the day its down to the client what they want testing and thats what LIM and the comment sections are for
 

Reply to Condition Reporting on static caravan site customer wants only 10% testing ????? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Post in thread 'Ireland - Customers wanting receipts' by Risteard has been reported by Risteard. Reason given: Content being reported:
Replies
1
Views
97
hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site. ive got tncs...
Replies
32
Views
7K
Hi Guys. Here's a good one for you, to rack the techies brains out there. Any views on the following please? By the way I'm NICEIC approved, Q.S...
Replies
20
Views
7K
We bought a decent condition touring caravan last year that had been recently serviced by a dealer and with a report basically saying among other...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock