Can anybody give the reg number that states that any conductor not connected whether in a multi core cable or single in a containment system should be connected to earth.
I may be wrong but as far as I am aware this is good practice and there is no reg stating it should be done.

Looking forward to being corrected.

thanks all.
 
They should be terminated for safety ... earthing is an option, just consider a fault between line and the unused core if it is floating around its potentially a hazard to someone; terminating the end and mark up as spare core if not to earth, any following sparks should still use safe testing procedures t won't be at added risk from it just floating about exposed end.
 
They should be terminated for safety ... earthing is an option, just consider a fault between line and the unused core if it is floating around its potentially a hazard to someone; terminating the end and mark up as spare core if not to earth, any following sparks should still use safe testing procedures t won't be at added risk from it just floating about exposed end.

same here capped and sleeved with heat shrink and labeled spare
 
The best way I’ve come across was the way I was shown as an apprentice.
Each core is terminated in order in what ever type of connection you are using. A 27 core, core 1 at the top, core 27 at the bottom or L>R. Any interconnects run in singles between the various multi core cables. Makes fault finding easy and looks good. You open a terminal chamber with 1000’s of terminals, you want some semblance of order not a rats nest at the bottom. We never earthed unused cores as many times we would be working on live systems, working from one end of a chain of TB’s to the other.

The bottom line, terminate them properly.
 
Thanks guys just as I suspected.
The reason I asked is that in response to a fault that was raised was that it is in the regs that spare conductors should be connected to earth.
I am unaware of any such reg or able to find one.
As the replays state it is good practise should any faults occur along with possible induced voltages that may be generated in a unconnected cable.

Thanks again
 

Reply to Conductors not connected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
923
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi All Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight...
Replies
55
Views
5K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock