Discuss Conduit factors in the Australia area at ElectriciansForums.net

L

Litttle Shonet

Good afternoon Gentlemen.I'm in the process of rewiring my garage so that I can join one of those fantastic schemes for my Part P.Question is this. looking at the OSG about conduit factors (Table 5D), it says about bends. Is this just bends in the actual conduit or does this include such things as 'elbows' and 'Tees'? The reson I'm asking is for example, it gives factors for 1metre runs with 4 bends, but none for 10 metre runs!!!Many thanks in anticipationLS
 
Tees and elbows should have inspection outlets which means you can pull in at these points so would not be included.

I remember, along time ago, attempting to pull through 20mm2 conduit, 3 * 2.5mm2 cables starting from a floor trunking 16m through 3.5 bends. I made the mistake of using a running coupler half way up the wall as opposed to a through box. I never did that again.

It doesn't take a very long length and a couple of bends to jam up the cables.
 
Last edited:
I never did get on with the newer conduit fill factor tables, it's like ''Double Dutch'' to me...lol!! I still use the old fill factor table as my starter guide, that and i suppose the experience that comes with the years of working on extensive conduit/trunking containment systems.
 

Reply to Conduit factors in the Australia area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
M
Hi Guys, I apologise in advance as I have done this a**se about face, I have just finished putting power to my shed ( I am currently training to...
Replies
34
Views
4K
F
Hi I am fitting conduit in my attic room ready for when i get it rewired so i can plaster up and have a finished room for the time being. I won't...
Replies
30
Views
5K
hi all first time i have posted, great site and lots of info cheers putting in for my assesment shortly with elecsa doing a c/u change and putting...
Replies
28
Views
44K
lauriehurman
L
hi have a query re conduit factors hope someone can help. OSG gives values for straight conduit runs between boxes, and values for conduit runs...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock