Discuss Consumer unit change testing in the UK Electrical Forum area at ElectriciansForums.net

That is not a method of testing, it is a method of calculating an estimated value.

It is not a viable method of attaining a value for the continuity of the CPC, for initial verification it is a requirement that the R1+R2 or R2 be measured prior to making a circuit live,

not sure thats fact dave, im sure it states, measure or calculate. If the earth path was compromised the zs reading would show this so its no different to R1+R2 and saves loads of time.
 
not sure thats fact dave, im sure it states, measure or calculate. If the earth path was compromised the zs reading would show this so its no different to R1+R2 and saves loads of time.

If you are not sure that what someone says is a fact it is customary to quote a fact to back up your contradictory viewpoint.
 
What about presence and adequacy of circuit protective conductors (411.3.1.1 543.1) if you are doing a EICR before replacing a consumer unit
 
I often take my feed for downlights in and out of a wago box and take a single T+E into the light fitting because its a lot easier at the fitting to get one cable in. See picture. Lets now say we only test R1+R2 at the last device or extremety of the circuit I will get the same reading regardless of whether or not I have the downlights fitted. Now add the downlights and make a poor earth connection in the wago box so the downlight is not earthed. R1+R2 is still the same and gives a good reading at the end of the circuit, but the downlight is not earthed. I have maintained earth continuity to the extreme end of the circuit through the wago box connections but failed earth between one of the wago's and a downlight. In a house with 30+ downlights I may have made more than one poor connection between the wago box and the downlight meaning I have 1+ downlights un-earthed.

Hence I always test R2 at every accessory, you may think this OTT but it is so quick its not worth not doing. Wander lead and test to a metal part on the light, I bet you could do 30 in less than 10 minutes.

Downlight.jpg
 
hi all I've got my first consumer unit change to do as I'm using this as my first nic assessment. My question is when doing my ir test the whole house is on led downlights about 30 of then plus under kitchen 12v led and a lot of sub sockets, will all,of theses need to be disconnected to do these test. Also do I need to do r1+r2 on every downlight.

Any advice is much appreciated as this is my first nic assessment after this change.

Thanks

I think everyone has missed the question though. I recently had my first inspection with NAPIT on a rewire and what they are actually looking for is understanding, not that you do it on the day. If you say to the inspector "Do you want me to remove all 30 bulbs to carry out the IR test or are you happy to see it with L-N shorted" I would be surprised if he would say take them all out. And contrary to what others have said earlier, you do need to test at 500v but if you short L-N and test to earth you can do this because you are not creating any potential between L-N. If you understand that you should test with them all out and individually test the line and neutral conductors he will be happy that you understand what you are doing.

With your R1+R2 don't do it. Do a wander lead test to measure R2 at each light fitting. You are only REQUIRED to do R1+R2 on ring final circuits as with the ring final you must test the continuity of every conductor, and this is due to the inherent danger of a ring circuit if a conductor fails such as a line or neutral. In a lighting circuit should your line or neutral conductor not be continuous, the lights won't come on, in a ring circuit should a L or N conductor not be continuous, everything will still work correctly however you could be overloading the one continuous leg of the ring if you fully loaded it.

A bit of advice for the inspection is that provided you understand what you are doing and why you are doing it you will be fine. If you are limited by the fact that everything is second fixed and you are passed initial verification stage then explain to him what you did at initial verification stage and why you think it is not practical to do that test now. Offer him the opportunity to do it if he wishes but they are not monsters he won't want to see you removing all 30 lights.
 
Hence I always test R2 at every accessory, you may think this OTT but it is so quick its not worth not doing. Wander lead and test to a metal part on the light, I bet you could do 30 in less than 10 minutes.


I'm a fan of the wander lead myself :)
If I'm unfamiliar with an installation (meaning I'm concerned it could be nasty) I often take a little walk around with Wanda and confirm what is connected to what.
 
I was looking at my wander lead the other day and wondering why I hadn't thought of adapting a regular 50m mains extension lead to do the job? All I need is an adapter at each end to bring out the earth pin to 4mm and I'm good to go.
The resistance would be lower if I parallel all three cores up but that represents a slight issue if somebody plugged the other end in by mistake...
But for the money they ask for a wander lead ....
 
get back in your cave troll

No need for silly comments like that mate it just derails the thread. Lets keep it professional guys.
Onwards and upwards!!!
 
I was looking at my wander lead the other day and wondering why I hadn't thought of adapting a regular 50m mains extension lead to do the job? All I need is an adapter at each end to bring out the earth pin to 4mm and I'm good to go.
The resistance would be lower if I parallel all three cores up but that represents a slight issue if somebody plugged the other end in by mistake...
But for the money they ask for a wander lead ....
The resistance does not matter - Either zero it on your meter or deduct it from your measured value. You are right though they do charge an awful lot for what they are...
 
I think this thread got derailed after the first page, when it went off on a tangent.

OP have your questions been answered, or are you more confused than when you opened this thread :confused:
 
I think this thread got derailed after the first page, when it went off on a tangent.

OP have your questions been answered, or are you more confused than when you opened this thread :confused:

There has been a lot of help with my questions I have now done the change and everything was fine now just got to wait for the assessment next week fingers crossed but with others I have spoken to and seen my work all say there is no reason it shouldn't go smoothly. I'm sure I'll have more questions to come but everyone on here's seems helpful and freindly so I won't be afraid to ask.
 

Reply to Consumer unit change testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hi, NAPIT report was carried out due to flood, all kitchen appliances, wall/light switches, fire/heaters etc need replacing. The electrician...
Replies
4
Views
903
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock