In some older houses you have the airing cupboard in the bathroom with all the immersion switches and pumps and sometimes the heating JBs all slung in there etc

Being in a cupboard arguably takes it out of the zone in the same way a FCU being under a bath does, and in the same way an airing cupboard/partition door does.
 
I was asked to fit a socket under the bath for a shower pump last week, I agreed to put a RCD spur in the hall with a flex from it and wiska box under the bath. It would have been unnecessary risk to have it under there.
 
Being in a cupboard arguably takes it out of the zone in the same way a FCU being under a bath does, and in the same way an airing cupboard/partition door does.
The only problem I see with the cupboard door argument is say the home owner is in the bath/shower the lights trip , they lean over and reach to the consumer unit and get a 240v belt while resetting the breaker Would a the cupboad door argument hold up in court
 
I was asked to fit a socket under the bath for a shower pump last week, I agreed to put a RCD spur in the hall with a flex from it and wiska box under the bath. It would have been unnecessary risk to have it under there.
If it wasn't acceptable, we probably wouldn't have whirlpool baths.
 
The only problem I see with the cupboard door argument is say the home owner is in the bath/shower the lights trip , they lean over and reach to the consumer unit and get a 240v belt while resetting the breaker Would a the cupboad door argument hold up in court
Unlikely to happen thought isn't it, probably more chance of slipping in the bath in the dark.
 
A lock on the door would solve the accessable without a tool issue and I doubt it is going to get wet. It is poor whatever way you look at it.

It could be relocated to the ceiling 😁.
 
A lock on the door would solve the accessable without a tool issue
I'm happy to be corrected, but what "accessible without a tool issue"? Completely from memory I thought that pertained to enclosures/junction boxes and I'm not picking up the relevance to this situation.

Regarding relocating it, I'd have thought the first question is whether it's currently on an external wall. If not the room behind the wall is the obvious choice.
 
I'm happy to be corrected, but what "accessible without a tool issue"? Completely from memory I thought that pertained to enclosures/junction boxes and I'm not picking up the relevance to this situation.

Regarding relocating it, I'd have thought the first question is whether it's currently on an external wall. If not the room behind the wall is the obvious choice.
Your right the without tool thing was referring to bath panels not cupboards. I still feel limiting access could make this a C3 instead of 2.
 

Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
746
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
3K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
773
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
865
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock