Discuss Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

That would help, however where in the regs dose it define a tool or a key as being a way of avoiding zones?
It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.

I'm just playing devil's advocate here, there's no way I would want a consumer unit anywhere in a bathroom.
 
What’s your thoughts of a new renovated house that has the consumer unit in the bathroom. It’s situated above the bath in a cupboard. It was brought 2 weeks ago and have no certs. They want a Eicr done. Obviously the sockets has to go too.

Thanks
Who is the they that wants the eicr done?
 
Rather than trying to code against 7671, why not just go for that jugular; EAWR Regulation 5 and 6 (Strength & Capability and Adverse or Hazardous Environments) as these apply while you are AT WORK undertaking the EICR. If we must put a reg against it then I offer up 132.5.1; Electrical Installation must be suitable for the environment for which it is located and expected to operate in
 
I’m away and don’t have the book with me however from memory I think 701 discusses walls and partitions, not cupboards. What this mostly boils down to is suitability for the environment, which is a clear fail. However I’m also caused to question if it’s going to satisfy the requirements for all wiring to be RCD protected - I’d have thought the incomer is highly unlikely??
 
Non sparky comment :
Irrespective of regs, I would have expected a survey to have alerted me to the issue and consequently would have purchased only if I could afford to get it moved.
I would immediately secure the doors and put a warning notice on them. Despite this I would worry about condensation.
Would an IP?? Enclosure prevent high levels of humidity around the electronics of rods/rcbos etc.? Or do they run warm enough even at zero load that I should not be concerned?
Personally, my sparky would have to work hard to convince me NOT to move it. An elcr would presumably help sparky to determine how problematic a move is likely to be .
 
I’m away and don’t have the book with me however from memory I think 701 discusses walls and partitions, not cupboards. What this mostly boils down to is suitability for the environment, which is a clear fail. However I’m also caused to question if it’s going to satisfy the requirements for all wiring to be RCD protected - I’d have thought the incomer is highly unlikely??

An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.

An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.

Electrical equipment under a bath is also compliant.

An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.

Because is behind a barrier, it's technically not in a zone.

If not in a zone, then IP rating etc shouldn't be an issue. ?
 
An outlet socket on a landing directly outside a bathroom door less than an MTR away would be compliant as it's behind a door.

An airing cupboard with electrical heating etc in a bathroom behind a door is compliant.

Electrical equipment under a bath is also compliant.

An electric shower which has just a plastic cover and also has uninsulated connections inside is also compliant.

Because is behind a barrier, it's technically not in a zone.

If not in a zone, then IP rating etc shouldn't be an issue. ?
See #38. Is said cupboard providing an  EFFECTIVE barrier.
 

Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
746
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors...
Replies
23
Views
3K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
773
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
866
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock