Discuss Contactor Coil Current Rating? in the Commercial Electrical Advice area at ElectriciansForums.net

joel89

-
Reaction score
14
Just out of interest what current does an AC Contactor coil take? I keep using 300va transformers in my panel builds but never take coil currents into account mainly only have up to 8 contactors. Cheers
 
It will have it written somewhere on the contactor, or in the data sheet with it.

Remember building panels to design your control Tx for all the items, plcs indicator lamps etc...

Most of our motor mccs use a 3kva Tx.
 
Just out of interest what current does an AC Contactor coil take? I keep using 300va transformers in my panel builds but never take coil currents into account mainly only have up to 8 contactors. Cheers

Measure the resistance of the coil then use good old ohms law.
 
Rated coil consumption of the Schneider LC1D09 thru LC1D38 contactor, 50 or 60 hertz AC control
70VA inrush, 7.5VA sealed
Was told by a transformer manufacturer your typical control transformer is good for three time rated va for inrush of contactor coils
 
Ask your wholesaler for schneider catalogues they have loads of info coil va, contactor ratings for AC and DC, resistive and inductive loads lots of bedtime reading one catalogues in particular to ask for is The essential guide to automation
 
Contactors and relay coil currents vary between products and ranges -their is no 1 answer.... check the info supplied or go on their website - AC / DC and voltage rating will have large effect to the nature of the coil resistance

Typical values for small relays 12/24v ac/dc are 0.5 to 1.5 watt and 230v 1-5VA but again i stress its variable

Inrush also varies as with coil resistance but typical 5-10 times on inrush.
 
Last edited:
I was going to comment, but there seems no more to say, apart from if he is using 400V control for his panels then he is breaking the law if he supplies them to anyone, including himself!
 

Reply to Contactor Coil Current Rating? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
440
At the weekend I installed a new bow thruster, 2 new batteries and a BatteryProtect 220A. The bow thruster does not work, I just get a clunk from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock