Discuss contactor rating in the UK Electrical Forum area at ElectriciansForums.net

S

Shaun12

When looking at contactors, does the coil voltage refer to auxiliary a1/a2 such as 24v supplied from a plc output and contact voltage rating refers to the feed/load being switched? If a contactor is rated to 690v/3-pole could it be used for 415v/3pole or 230v single pole?
 
A1 & A2 are the coil voltage to operate the contactor, the voltage switched is only relevant to the current being switched. So the voltage is not a issue, as the contactor rated for 690v will switch any voltage below its rating. The current rating will however decrease on lower voltage and if used for DC switching
 
Any voltage can operate a controlling coil for a contractor switching any voltage.

It should noted though that many old contactors may still have a 240/415v coil

You must make sure though that all supplies are from the same main source of supply even if a transformer is used, if not it should be indicated that there are 2 sources of supply.
 
Last edited:
The current rating will however decrease on lower voltage

Don't understand this bit Tazz, did you mean to say the power rating?
 
Thanks for the replies.

Would this be classed as a contactor?
What is the part sitting out from the main unit?

8cebb694e85583ceda959d248c363093.jpg
 
Thanks.

Oh what's the difference then? They both operate in the same way with the same idea a coil making contacts when energised. So when does a relay become a contactor?
 
Contactors have the ability to switch higher currents and are made to suit whilst relays normally switch much lower currents such as control circuits etc. You can purchase mini contactors which are the same form factor as the relay you have there.
What is it you are wanting to do with this?
 
Last edited:
These are seimens range of compact contactors and usually for the lower loads ...as for the difference between them well I never really thought about it, but often relays tend to be limited load handling ...

This isn't technical but if clicks, its a relay and if it clunks, its a contactor ;) (Excluding solid state device before I get a smart comment :p)
 
Thanks.

Oh what's the difference then? They both operate in the same way with the same idea a coil making contacts when energised. So when does a relay become a contactor?

Generally speaking a contactor is used to switch a load and a relay is used within control circuits.
But there is no hard and fast definition to either.
Generally contactors have higher current ratings and switching duties, but you can also get relays capable of switching 100's of amps.
 
The tell-tale sign in your picture are the markings, these denote normally open and normally closed contacts which are usually found on relays of that type, contactors on the other hand are marked up differently L1, L2, L3 etc.
 
The tell-tale sign in your picture are the markings, these denote normally open and normally closed contacts which are usually found on relays of that type, contactors on the other hand are marked up differently L1, L2, L3 etc.

That doesn't necessarily make it a relay though, it could still be a contactor.

Some of the other writing on there is a bit more useful in getting reliable identification, specifically the part number. A quick google brings up a data sheet clearly tilted 'contactor'
 
These are seimens range of compact contactors and usually for the lower loads ...as for the difference between them well I never really thought about it, but often relays tend to be limited load handling ...

This isn't technical but if clicks, its a relay and if it clunks, its a contactor ;) (Excluding solid state device before I get a smart comment :p)
clunk -click. thought jimmy saville was brown bread.
 
I'd say it's a contactor, that's what I ask for when I need one of these lol, relay and contactor are essentially the same thing, as has been said it is usually higher switching currents with a contactor, but whatever the manufacturer calls it.......
 
I didn't realise a contactor could be switched using Normally open Or normally closed contacts like a relay can be switched, I thought they were coil controlled?
 

Reply to contactor rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
604
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
Replies
0
Views
495
Hello, I’m need some advice on how a contactor is wired please and where the neutral go. I’m told it is connected to eco 7 and controls 3 heaters...
Replies
12
Views
3K
Hi. Can anyone offer a bit of advice please. I've got a customer who wants needs an upgrade to their consumer units. It is a bungalow that has a 3...
Replies
11
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock