Hi all,

I'm hoping there is something I can do to make this work without having to run 14/3 from switch to switch. I've attached my simple sketch of what I am working with but essentially everything has 14/2 running to it and 14/2 goes switch to switch.

From what I can tell this would be possible if the wire going to the light was in the box opposite of where the power comes into but I'm struggling to figure out if there is anything I can do.

Any help would be greatly appreciated!
 

Attachments

  • Screenshot_20211208-200506_Keep Notes.jpg
    74.8 KB · Views: 6
To make the switches work as 3 way (2 way in the uk) you need 3 cores between them plus whatever is used as ground.

If the far away switch could get a hot (live) from another nearby source on the same circuit, the 2 cores you have could be used as travellers (strappers)


How’s my translation, @Megawatt ?
 
To make the switches work as 3 way (2 way in the uk) you need 3 cores between them plus whatever is used as ground.

If the far away switch could get a hot (live) from another nearby source on the same circuit, the 2 cores you have could be used as travellers (strappers)


How’s my translation, @Megawatt ?
My friend I’m sorry to tell you this but you have to have 14/3 to make 3 way switches work correctly as @littlespark stated above. Thanks for the help @littlespark.
 
To make the switches work as 3 way (2 way in the uk) you need 3 cores between them plus whatever is used as ground.

If the far away switch could get a hot (live) from another nearby source on the same circuit, the 2 cores you have could be used as travellers (strappers)


How’s my translation, @Megawatt ?
@littlespark thanks. At the far switch I could possibly power it there. That is a 4 gang switch and there should be a power source.

Thanks alot! That could be an easy solution and I was just over thinking it.

I will reply after I'm able to take a look
 

Reply to Controlling a light with 2 switches (3 way with 14/2 wire) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
886
I took a light down to put up a new fixture and now the light goes on but the switch doesn’t shut the light off. The power only stays on so I am...
Replies
3
Views
2K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
344
Hi, Need some help with an odd setup. I have a large room with many lights that i separated into 2 sets. In Box 1 there is the 14/2 power in, 2...
Replies
4
Views
1K
DYI guy here with some basic knowledge of electrical craft. I am helping a buddy in his remodeled bathroom. His GFCI outlet was powered off vanity...
Replies
11
Views
983

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock