- Reaction score
- 0
Hi all,
Looking for some advice if possible please!
Got one if then jobs that you get roped in to and that’s turned from a quick simple tasks to maybe a small can of worms.
The customer wanted her oven connecting as curry’s have installed the hob but not the oven.
Cooker circuit - 32a breaker to a 45a cooker switch (no integrated socket) in 6mm twin and earth.
In the cooker switch the 6mm comes in and I found two 2.5mm twin and earth connected into the supply 6mm terminals also….
Investigated and one is for the extract (no fused spur and one is for a socket supply a washer/dryer, again no fused spur.
I work commercially so needing advice on this.
Hob - 5.8kw
Oven - 2.4kw
Fan - 0.15kw
Washer/dryer - can’t find load spec unfortunately - would probably have this down as 2.5kw-3kw
Let’s say we can allow this and can apply diversity and would allow all loads. I was thinking down the route of 6mm radial to three fused spurs so the socket, oven and extract cables were protected accordingly and not from the 32A breaker at the DB.
Any help advice much appreciated as domestically I’m very rusty!
The socket for the washer dryer wouldn’t be the easiest to connect into the kitchen ring so that’s why I asking for any other good and practical solutions.
Thanks!
Looking for some advice if possible please!
Got one if then jobs that you get roped in to and that’s turned from a quick simple tasks to maybe a small can of worms.
The customer wanted her oven connecting as curry’s have installed the hob but not the oven.
Cooker circuit - 32a breaker to a 45a cooker switch (no integrated socket) in 6mm twin and earth.
In the cooker switch the 6mm comes in and I found two 2.5mm twin and earth connected into the supply 6mm terminals also….
Investigated and one is for the extract (no fused spur and one is for a socket supply a washer/dryer, again no fused spur.
I work commercially so needing advice on this.
Hob - 5.8kw
Oven - 2.4kw
Fan - 0.15kw
Washer/dryer - can’t find load spec unfortunately - would probably have this down as 2.5kw-3kw
- Is the extra socket for the washer dryer even permitted? Against regs etc as it’s not a cooking appliance.
- Are we allowed to apply diversity to this circuit m if I were to connect the oven. If so, would it be a cooker circuit diversity or other?
Let’s say we can allow this and can apply diversity and would allow all loads. I was thinking down the route of 6mm radial to three fused spurs so the socket, oven and extract cables were protected accordingly and not from the 32A breaker at the DB.
Any help advice much appreciated as domestically I’m very rusty!
The socket for the washer dryer wouldn’t be the easiest to connect into the kitchen ring so that’s why I asking for any other good and practical solutions.
Thanks!