Search the forum,

Discuss Cooker Circuit with Washer/Dryer On Circuit in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
0
Hi all,



Looking for some advice if possible please!



Got one if then jobs that you get roped in to and that’s turned from a quick simple tasks to maybe a small can of worms.



The customer wanted her oven connecting as curry’s have installed the hob but not the oven.



Cooker circuit - 32a breaker to a 45a cooker switch (no integrated socket) in 6mm twin and earth.

In the cooker switch the 6mm comes in and I found two 2.5mm twin and earth connected into the supply 6mm terminals also….

Investigated and one is for the extract (no fused spur and one is for a socket supply a washer/dryer, again no fused spur.



I work commercially so needing advice on this.



Hob - 5.8kw

Oven - 2.4kw

Fan - 0.15kw

Washer/dryer - can’t find load spec unfortunately - would probably have this down as 2.5kw-3kw



  1. Is the extra socket for the washer dryer even permitted? Against regs etc as it’s not a cooking appliance.
  2. Are we allowed to apply diversity to this circuit m if I were to connect the oven. If so, would it be a cooker circuit diversity or other?




Let’s say we can allow this and can apply diversity and would allow all loads. I was thinking down the route of 6mm radial to three fused spurs so the socket, oven and extract cables were protected accordingly and not from the 32A breaker at the DB.



Any help advice much appreciated as domestically I’m very rusty!

The socket for the washer dryer wouldn’t be the easiest to connect into the kitchen ring so that’s why I asking for any other good and practical solutions.



Thanks!
 
There is no definition of a “cooker circuit”. What you are looking at is a radial circuit with a number of items attached to it.
Sure you can have a socket on a circuit like this. Many “cooker” isolation switches also have a socket on them. The plates are not engraved “cooking appliances only”. You could plug in a kettle, or a dishwasher. Nobody’s going to report you to the circuit police.

Personally I would do my normal diversity/ max demand calcs for the radial and crack on.
 
There is no definition of a “cooker circuit”. What you are looking at is a radial circuit with a number of items attached to it.
Sure you can have a socket on a circuit like this. Many “cooker” isolation switches also have a socket on them. The plates are not engraved “cooking appliances only”. You could plug in a kettle, or a dishwasher. Nobody’s going to report you to the circuit police.

Personally I would do my normal diversity/ max demand calcs for the radial and crack on.
Thanks for the reply!

Just was doubting myself since it’s not something I something have to worry about.
Cookers are three phase where I work!

If I diversity for a cooker circuit i get 30 amps and for a radial I get 34amps.
Could in theory upgrade to a 40A breaker but a bit reluctant to!
 
If I diversity for a cooker circuit i get 30 amps and for a radial I get 34amps.
I’m not aware of any difference in diversity calcs based on circuit type. It’s done by appliance. Since a cooker circuit IS a radial anyways?
Could in theory upgrade to a 40A breaker but a bit reluctant to!
Subject to the usual cable installation type considerations. It’s an easy fallback should problems arise later.
 

Reply to Cooker Circuit with Washer/Dryer On Circuit in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I've got a new oven and have a question about installing it. It's a 2.6kW 13A oven, and a cable from the 32A cooker circuit to...
Replies
4
Views
384
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
865
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
695
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock