Discuss Copper Surface Trunking in the UK Electrical Forum area at ElectriciansForums.net

B

Broomstick

Hi
i have an old stone cottage. I need to do some surface re-wiring but I do not like plastic trunking. Could I use copper piping for the wires as I feel this would make a good feature. Would this be safe.?
 
Metal conduit is perfectly safe so as long as it's properly installed I don't see a problem. You may struggle to get fittings for it to get it to fit to boxes
 
Metal conduit is perfectly safe so as long as it's properly installed I don't see a problem. You may struggle to get fittings for it to get it to fit to boxes

you can get 15mm tank connectors to connect back boxes but its a right old headache and i think the only way to make look neat is to solder joints rather than compression joints
 
I think plastic compression joints may look a bit odd...
 
Theres some great paint products about now and i reckon if you did it in white plastic conduit then primed it well you could get a copper affect paint for it look for metal kote paints (think thats the name)
 
Have you considered using mineral?

Cables contained within exposed copper but all in one. No need for joins and no need for special bending tools. IMHO it would look way better than using plumbing pipe and joins for electrical equipment!
 
ANd the latest price of MICC is .... ?

Only about £5-6 per meter at the most expensive suppliers. Not exactly a bank breaking amount of money for a little surface wiring.

And if you don't terminate properly (not a DIYer job) the while lot shorts out. Nice idea, but surely only for deep-pocket specialists

For a start, a DIYer shouldn't be touching electrics in the first place and I'd like to think anyone calling themselves an electrician should be able to properly terminate mineral cable. It's not exactly hard is it, just more time consuming than working with other types of cable.

I only mentioned it coz the OP seemed like he wanted a proper and safe job doing that looks the part too. IMHO, mineral is the only way to go :)
 
Hi
i have an old stone cottage. I need to do some surface re-wiring but I do not like plastic trunking. Could I use copper piping for the wires as I feel this would make a good feature. Would this be safe.?

Copper pipes a good feature :eek: I am absolutely amazed by that decision,but each to their own I suppose


You would be well advised (in my opinion) to consider mineral as D Skelton suggested
Considerations about poorly terminated ends would only arise if it was done without experience
It would mean paying a spark with the skills,but surely,if aesthetics are that important,then it would be a thousand times better
 
I was thinking of MI as well. If the customer can afford to be picky about the look they can afford MI. The advantages being MI is a 'recognised' wiring method as opposed to using plumbing pipe as conduit, and it's going to be much easier and neater to dress around corners, irregular angles etc.
 
commonly known as pyro cable. it's got it's own copper sheath/outer covering. you can get it also with orange plastic coating, but you don't want that!.
 

Reply to Copper Surface Trunking in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing some work in a commercial restaurant/kitchen the builders had already boarded and plastered the walls meaning my only viable route is to use...
Replies
31
Views
1K
Good afternoon, I wanted to heat up a .5" copper tube that is approximately 15cm long up to about 250 C. I would like to use nichrome to do...
Replies
4
Views
568
Hi all, question on extending an existing ring main onto the surface and then re-joining back to in-wall. Is there a ‘correct way’ to do this, as...
Replies
5
Views
1K
Hi Everyone, Sorry if this is a silly question. I am supporting my mum with some small home renovations, in preparation for a care home. I am...
Replies
4
Views
691
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock