fourtytwo

DIY
Reaction score
25
Good evening everybody. I have a cooker feed from the CU that is then split under the floor above the kitchen to separate outlets for the hob & Oven. The problem is a standard 30A JB does not have big enough terminals to accommodate the wires. The person who installed this has cut some of the strands and one of the terminals appears cross threaded in the attempt. I am just about to close the floor permanently with wretched laminate and am not happy to leave this as is under the floor, any suggestions how to improve it ?
 

Attachments

  • P1170556.JPG
    874 KB · Views: 35
  • P1170557.JPG
    925.5 KB · Views: 33
That joint will need to be 'maintenance free' and that joint box is not suitable. What you are trying to do is a disaster in waiting.
 
That joint will need to be 'maintenance free' and that joint box is not suitable. What you are trying to do is a disaster in waiting.
Umm not what I am trying to do, I am trying to do the job correctly after discovering this under the floor!
Exactly what MF connectors are you suggesting are suitable ?
 
Those junction box terminals sometimes splay open as you torque them. As Westwood says a maintenance free box should be used if it's not going to be accessable.

I'm in Norfolk too btw.
 
Last edited:
Umm not what I am trying to do, I am trying to do the job correctly after discovering this under the floor!
Exactly what MF connectors are you suggesting are suitable ?
Are they 6 sq mm conductors?
If so I'd be looking at Wago 221-613 3-way connectors, with each cable being clamped at point of entry to an adaptable box (Wiska or similar)
 
As above, you can't leave that junction box under the floor. Regardless of how well it is fitted.
 
Are they 6 sq mm conductors?
If so I'd be looking at Wago 221-613 3-way connectors, with each cable being clamped at point of entry to an adaptable box (Wiska or similar)
Hi Tim, yup I guess there 6mm sq although they predate such measures being black & red insulation. Thanks for giving me the wago part# unfortunately the likes of screwfix only sell them in packs of 50 so now I just have to hunt down a source of a few and a box. We have a local electrical wholesalers but they will probably laugh at me but worth a try....
 
You need to double check the part numbers as the do ones that only accept upto 4mm. Screwfix sell the right ones in packs of 30.

The wago XL box is only rated for 4mm cables but it's probably the best option.
 
Hi Tim, yup I guess there 6mm sq although they predate such measures being black & red insulation.
The UK went metric in conductor size in the early 70s but did not harmonise colours to the current form for fixed wiring until around 2003 (I think)
Thanks for giving me the wago part# unfortunately the likes of screwfix only sell them in packs of 50 so now I just have to hunt down a source of a few and a box. We have a local electrical wholesalers but they will probably laugh at me but worth a try....
Be careful with "maintenance free" parts as often the box is only certified as MF with specific terminals and often with the addition of a cable tie to keep the lid in place no matter what.

Basically read the instructions carefully before you decide and act.
 
Anything above 4.0 it starts getting difficult. I would solder butt the conductors and encapsulate the enclosure.
 
Anything above 4.0 it starts getting difficult. I would solder butt the conductors and encapsulate the enclosure.
I must confess I have not actually measured it to know what cross section it actually is, whatever it is 3 lots of it simply dont fit properly in a 30A JB.
 
The lower left cable is no bigger than 6.0 but the other cable has tinned copper conductors and is likely to be imperial, above 6.0 but less than 10.0 judging by its apparent size.
 
This one says 6mm and has MF instructions:
But only with this connector for 32A use:
A search around might find other cheaper suppliers, but in the grand scheme of things it is not too much to spend.
 
A Knightsbridge 60amp junction boxes are much better than what you have but are not maintenance free/screwless terminals. I would use them in a loft when extending electric showers.
 
Status
Not open for further replies.

Reply to Correct way to joint 3 x 30 Amp cables, 30A JB not big enough in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

S
Back to my cat pee soaked floors and a RCBO protected radial cirucit that is giving grief. RCBO symptoms described by the customer, "it's a...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock