A number of 3 phase induction motors and a single phase motor are fed via a p.t.o driven generator. There is a small current imbalence between the phase feeding the single phase motor and the other 2 but this i think is acceptable. How much of a current imbalenbce in amps (A) would be deemed dangerous to the generator either over heating or in worsed case scenario blowing a winding if all circuit protection fails. Also how long would it take to cause such damage if the generator is in constant use?
 
What are your generator tolerances? Do you have a programmable Generator protection relay or some sort of command control system on the generator itself?

Every generator manufacturer will have their own tolerances built into their generator and current unbalance will be one of them. You will need first off to contact the generator manufacturer and get their tech specs.

The negative-sequence component (I2) of stator current is directly proportional to the load unbalance and sets up a counter acting flux field in the machine. This in turn cause heating in the rotor iron and then severe damage

The capability of a generator to withstand heat caused by unbalance currents is typically experessed in terms of an constant, and is supplied by the manufacturer of the machine.
 
Would be nice to know what sort of imbalance your talking about seeing on your generator!!

Much more info is needed, like what is the KVA rating of the Genny, what are the loadings of these 3 ph and 1ph motors. What sort of duty cycles your working too, or are these motors constantly running??


By the way, what does p.t.o mean?? Is it ''Part Time Operation''?? If so, do you mean this Genny is a stand-by power source??
 

Reply to Current imbalence in a 3phase p.t.o driven generator. in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
I don't normally get involved with domestic work but this job is for a family member so I cant Simpley say no. the house is a large property with...
Replies
3
Views
1K
Hi all, Been a few years since i've posted but here goes! At the factory I work in we have an old Spanish line from the mid-eighties that is fed...
Replies
6
Views
5K
M
hi everyone we have a three phase supply (63 amp hrc fuses) which feeds a star delta motor control panel with interlocking door panel switch...
Replies
2
Views
1K
maddfridge
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock