Hello ?,
is there any regulation of wire cross section for current transformers? Somewhere I read that wires from transformer to Amp meter (for example) should be minimum 2.5mm2, but on some other site I read that it must be minimum 4mm2 ?. I don't know where I read it, but I read it.
What is your opinon, which one is correct? Is there any regulation?
Tnx!! ?
 
Hello ?,
is there any regulation of wire cross section for current transformers? Somewhere I read that wires from transformer to Amp meter (for example) should be minimum 2.5mm2, but on some other site I read that it must be minimum 4mm2 ?. I don't know where I read it, but I read it.
What is your opinon, which one is correct? Is there any regulation?
Tnx!! ?
Not sure but you must remember\to provide a shorting facility from the CT leads just in case you need to remove the wiring from the Ammeter
 

Reply to Current transformer - wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hi All, I've installed a Lorex doorbell recently, but it is not turning on. I did some tests using a multimeter and this is what I found...
Replies
5
Views
1K
Hello, I would liked to install a Byron wired doorbell with built in chime and 8v transformer. I'm struggling to get power source. I have a...
Replies
1
Views
446
My friend has got one of those robot lawnmowers that automatically goes out once a day and runs around the grass. There is a single core guide...
Replies
7
Views
305

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock