Anyone had problems with these rcds? Control Gear Direct, 30mA, 63A 2 pole..
I recently bought two 10-way dual rcd boards from denmans.. first one had an rcd which didnt trip on test button, even with load removed. Second rcd didnt trip under 300mS, but button worked.
Swapped them for the rcds in the second board I had (lucky me, I thought).. one rcd was ok but second one also had trip time problem. swapped the rcds around and the problem followed the rcds.
Got denmans to hotfoot replacement two boards that day... one rcd no trip on test button, the other had trip time problem!
The rcd which "worked" ok, I subsequently found to be a bit intermittent also on trip time. Once i put it on x2 test it seemed to settle down. but also the test button sometimes takes a while to trip as well! ie had to hold it down for a second or two.. the test results when working show no unusual results, all appliances were disconnected.
I did wonder if my tester (metrel 31000) was beginning to play up but worked ok at home and was only calibrated a few weeks ago.
I also put in the only other rcd i had with me, a Hager, and this has been fine.
Control Gear have posted to me 4 replacement rcds with test results, so ill see what happens..
First time ive had NO Trip problems, usually the other way...
I recently bought two 10-way dual rcd boards from denmans.. first one had an rcd which didnt trip on test button, even with load removed. Second rcd didnt trip under 300mS, but button worked.
Swapped them for the rcds in the second board I had (lucky me, I thought).. one rcd was ok but second one also had trip time problem. swapped the rcds around and the problem followed the rcds.
Got denmans to hotfoot replacement two boards that day... one rcd no trip on test button, the other had trip time problem!
The rcd which "worked" ok, I subsequently found to be a bit intermittent also on trip time. Once i put it on x2 test it seemed to settle down. but also the test button sometimes takes a while to trip as well! ie had to hold it down for a second or two.. the test results when working show no unusual results, all appliances were disconnected.
I did wonder if my tester (metrel 31000) was beginning to play up but worked ok at home and was only calibrated a few weeks ago.
I also put in the only other rcd i had with me, a Hager, and this has been fine.
Control Gear have posted to me 4 replacement rcds with test results, so ill see what happens..
First time ive had NO Trip problems, usually the other way...