Hi all,

The dimmer push button still works but the dimmer stopped working when i turn the button, i heard a pop noise and it was then when it stopped working.

This is the second dimmer now and it has happened to both of them, not straight away, each one lasted about 4-5 weeks.

I wonder if it's got something to do with the bulbs as they don't last that long to be honest.

Here is all the information i can find on the dimmer/bulbs/light....

LAP G9 Capsule LED Light Bulb 300lm 3W 220-240V 5 Pack (7688V)

Specification:

Brand LAP
CALC - Light Bulb Technology LED
Cap Fitting Type G9
Colour Temperature Description Warm White
Colour Temperature Value 2700 K
Dimmable Dimmable
Energy Rating A+
Equivalent Wattage 30 W
Equivalent Wattage Band 21-30
kWh Per 1000hr Life 3 kWh/1000h
Life Length 15,000 hours
Light Bulb Technology LED
Light Bulb Type Capsule
Lm 300 lm
Lm Band 201-400
Manufacturer Guarantee 3 Year Manufacturer's Guarantee (T&Cs Apply)
Pack Size 5
Pieces in Pack/Case 5
Power Consumption 3 W
Power Factor Value Greater than 0.4
Power Voltage Supply 220-240 V
Product Diameter 16 mm
Product Length 49 mm
Product Type Light Bulb

British General 1-Gang 2-Way 400W Push Dimmer Switch White (65335)

Specification:

Brand British General
CE Standard (Tested to EN...) EN 60669-2-1.
Fixings Supplied Fixings Supplied
Insert Colour Without Inserts
Manufacturer Guarantee 25 Year Manufacturer's Guarantee (T&Cs Apply)
Max. Dimmable Load (Fluorescent) 100 W
Max. Dimmable Load (Halogen) 350 W
Max. Dimmable Load (Incandescent) 400 W
Max. Dimmable Load LED) 50 W
Min. Dimmable Load (Fluorescent) 10 W
Min. Dimmable Load (Halogen) 35 W
Min. Dimmable Load (Incandescent) 60 W
Min. Dimmable Load (LED) 5 W
Model No 981P
No. of Ways 2
Number of Gangs 2 Gang
Pack Size 1
Parent Colour White
Pieces in Pack/Case 1
Power Voltage Supply 240 V
Product Type Dimmer Switch
Screwed/Screwless Screwed
Smart Compatibility Not Smart
Suitable for Dimming LEDs LED
Switches & Sockets Finish Plastic
Switches & Sockets Product Type Dimmer Switch
Switches & Sockets Profile Type Raised Square
Switch Product Type Light

Light:

Specification:

Requires 5 x G9 Max 28W bulbs (not included).

Depth: 510 CM
Height: 150 CM
Material Content: Glass+Metal
Width: 510 CM
Indoor / Outdoor: Indoor
Maximum Wattage (in Kw): 28

Any ideas would be most welcome

All the best

Jay
 
try trailing edge dimmer like varilight .Trailing edge dimmers (aka “electronic dimmers”): The electrical current (sinusoidal signal) is turned off at the end of the AC input waveform immediately before the zero crossing Traditionally used for electronic drivers or low voltage transformers (capacitive loads).
 
Last edited:
You have the wrong kind of dimmer for the lamps, and it's probably poorly made anyway being BG
 
what's with all the negative waves with BG? I've installed loads of BG gear and never had any failures.
 

Reply to Dimmers keep failing after 4-5 weeks in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

The following light fitting from Dumelm takes GU10 but states "Dimmable No" but I can't see why with the correct dimmer switch and dimmable GU10...
Replies
2
Views
664
Hi all I am a newbie from Australia to this great forum. I need some advise with wiring up a dimmer and switch for my LED Down lights in...
Replies
12
Views
21K
Recently moved into a new home and replaced the main light fitting in the sitting room. We replaced it with this dimmable LED fitting: ENDON...
Replies
9
Views
3K
Hi All...FYI Im in the UK. I can do the basics and I have changed the dimmer in my kitchen a couple of times but it keeps failing. It runs five...
Replies
12
Views
4K
Having a bit of a nightmare with what should have been a simple job. Back in January I replaced some old Varilight dimmers which had failed after...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock