Discuss Dimplex Quantum QM150 Storage Heater Off-Peak Supply Wiring Help in the Electricians' Talk area at ElectriciansForums.net

B

bigp26

Hi All,

I hope you are all enjoying your weekends!



Before I start, I just want to thank you for your help in advance…

To summarise, I had storage heaters installed a few weeks ago by an installer, and have experienced a few problems!

To cut a long story short, the flat I moved into used to have horrible storage heaters in the living room and hallway, which I replaced with electric panel heaters. I was told that my bills would go sky high (which they did), however at the time, I was a bit stuck as my refurb budget had run out.



Fast forwarding to a few weeks ago, I had 3 Dimplex Quantum heaters installed. Now the Quantums in the living room and hallway seem to be fine (as the off-peak supply was already there, ready to be connected up via a fused spur), however the bedroom Quantum has given me some issues.

As there was no storage heater in my bedroom before, there was no off-peak supply. As such, the electrician made the suggestion of simply plugging the off-peak element end of the heater via a normal 3 pin plug into a normal socket, via an electronic timer (to emulate the switching at off peak times to take advantage of Economy 10).

I asked him if this was safe, and he said yes it was safe, and that it is a much better solution than having to pull a new cable from the other side of the property (literally the other side!). This gave me comfort as I know this electrician also performs electricity safety tests for properties. The DImplex Quantum QM150 was therefore installed in my bedroom using this setup.



Now for the issues:

1) About 2 weeks ago, I found that the heater wasn’t charging up with off-peak electricity, and thus wasn’t giving out any heat at any time.

Having investigated this, I found that the switch for the socket that the 3 pin plug was plugged into, was stuck. I was thus unable to switch it from on and off.

To test this, I plugged in my iPhone charger and confirmed that no electricity was being output even with the switch in the on position. I put this down to a cheap switch that had gone faulty, and simply replaced it.



2) Last night, I could hear some buzzing/crackling from the off-peak socket whilst I was in bed. I therefore went closer to investigate, and smelt a little bit of electrical burning (similar to when using a soldering iron). As such, I quickly turned the switch off and took the plug out of the socket.

What I found was that the front of the timer socket (i.e. where the 3 pin plug goes into), was very slightly melted. I also found that the plug was slightly melted on the neutral side. Opening the plug up, I could see that there was damage on the neutral connection of the pin (i.e. to the plastic and screw etc.). Obviously the front of the plug was warm to touch at this point too.​



This has made me extremely worried, and I have been doing a few hours of research this morning.

I understand that the off-peak elements of storage heaters are not really suited to be simply plugged into normal sockets (apologies if my terminology is incorrect, but I understand that the normal sockets are connected to the 30A ring main, and similarly, off-peak elements shouldn’t be connected to 30A ring mains).

I have also read that the storage heaters should be connected with 2.5mm wire (both from the heater to the socket, and from the socket to the fuse box).



So I’m just weighing up my options before I go back to the install company and start making a fuss:


Option 1:

I noticed that the connection between the plug and the timer socket wasn’t great i.e. the pins didn’t sit completely flush into the socket, but sat with a 1-2mm gap. Assuming that this was the issue (i.e. poor connection), the first option is to replace the plug and replace the timer with different models, which are a bit more compatible with each other and therefore don’t exhibit the 1-2mm gap.


Option 2:

Get rid of the socket and the plug, and replace this all with a Greenbrook T205-C Fused Timer Spur.


Option 3:

Ask the installer to come back and put in a new 2.5mm wire from the off-peak supply fuse box to my bedroom.


Out of the 3 options, my least preferable option is number 3, as the fuse box and the bedroom are literally on opposite sides of the property, which will mean lots of ugly trunking.

Option 2 therefore makes the most sense to me, but obviously this means that the off-peak element is still using the 30A ring main. The wire going from the heater to the socket looks like 2.5mm to me, but I think the wire going from the fuse box to the socket looks like 1.5mm (I’m not 100% sure about these wire sizes though – any easy way to confirm?). Considering these points, should this setup be OK?



Thoughts and suggestions would be much appreciated.

Kindest regards!
P.
 
Last edited by a moderator:
IMHO you should get the original installer back or get a 2nd opinion, but I think running an additional off peak supply is probably the best option.
 
The QM150's storage input (if I remember rightly) is 3.3kW which translates to about 14A (voltage dependant). This obviously means you will have issues with any workaround involving a fuse. It should be supplied from a 20A dp sw on a dedicated circuit, meaning the only option for me would be number 3. It would also be worth noting that it's not common practice to have storage heaters in bedrooms although this doesn't mean you shouldn't.
 
Why isn't it common practise for storage heaters in a bedroom Resu? I just wondered........
I'm not sure tbh. I have worked in/tested hundreds of properties with E7/E10 or THTC setups and not one of them had storage heaters in the bedrooms, it was always panel heaters in the bedrooms. Thus leading me to believe it wasn't common practice!
 
IMO. option 3, and as resu's post, a 20A dedicated circuit.
 
Many thanks for your advice so far. Very much appreciated.

I've been exchanging emails with the installer all day, so I thought I would provide an update.

They have been very apologetic, and the last email I received said the following:


"Can you tell me what series your heater is please? (Under the flap on top it should say Series G or F or E, etc. If it is a G it can be programmed without the use of a timer.

If it is not a G then it will need a suitable timer capable of switching 3.3KW wired in correctly to a 20amp double pole isolator.

The heater will also need the 24hr supply for the timer/programming side which you already have with the socket outlet.

This arrangement has been okayed by Lawrence at Dimplex providing that the off peak supply isn’t on a plug top and correctly isolated (20amp double pole isolator)."

Any thoughts from you experts?
 
Thanks Murdoch! In a bit of a strange situation now as the installers are quite reputable in the area, and if I were to go elsewhere I would have to pay again (having already forked out over a couple of grand with these guys). I would have thought they would have been able to do a proper job/give sound advice, but seemingly not!

Find an electrician who knows what he is doing!
 
Thanks Murdoch! In a bit of a strange situation now as the installers are quite reputable in the area, and if I were to go elsewhere I would have to pay again (having already forked out over a couple of grand with these guys). I would have thought they would have been able to do a proper job/give sound advice, but seemingly not!

Who made the decision to spec the specific heater? Seems to me that this is the problem.... or rip the thing out and fit a panel heater with a timer!
 
Dimplex themselves spec'ed the heater having been provided with my floorplan and room sizes.

Problem is that I actually had a panel in the bedroom before, but thought I would get the Quantum installed as I was getting the other 2 installed anyway, and thought I'd make that extra investment for the longer term saving (my bills were sky high with panels all around!).

Who made the decision to spec the specific heater? Seems to me that this is the problem.... or rip the thing out and fit a panel heater with a timer!
 
Many thanks for your advice so far. Very much appreciated.

I've been exchanging emails with the installer all day, so I thought I would provide an update.

They have been very apologetic, and the last email I received said the following:


"Can you tell me what series your heater is please? (Under the flap on top it should say Series G or F or E, etc. If it is a G it can be programmed without the use of a timer.

If it is not a G then it will need a suitable timer capable of switching 3.3KW wired in correctly to a 20amp double pole isolator.

The heater will also need the 24hr supply for the timer/programming side which you already have with the socket outlet.

This arrangement has been okayed by Lawrence at Dimplex providing that the off peak supply isn’t on a plug top and correctly isolated (20amp double pole isolator)."

Any thoughts from you experts?

So dimplex have pretty much confirmed that you need the job to be done properly and not bodged via a plug, since you can't fit an unused 20A DP switch directly to the ring circuit.
I think you should be getting the original installer back to do the job properly at their own cost seeing as they deliberately overloaded a 13A socket and created a fire risk.
 
Ahh - didn't realise the 20A DP switch can't be connected to a ring main, but thinking about it now it kind of makes sense.

The installer obviously doesn't know this however, as they have taken Dimplex's advice as being (in simple terms): where the plug was plugged in via a timer, remove the plug socket, replace with a 20A DP switch, and connect the off-peak element to the new switch.

So dimplex have pretty much confirmed that you need the job to be done properly and not bodged via a plug, since you can't fit an unused 20A DP switch directly to the ring circuit.
I think you should be getting the original installer back to do the job properly at their own cost seeing as they deliberately overloaded a 13A socket and created a fire risk.
 
So dimplex have pretty much confirmed that you need the job to be done properly and not bodged via a plug, since you can't fit an unused 20A DP switch directly to the ring circuit.
I think you should be getting the original installer back to do the job properly at their own cost seeing as they deliberately overloaded a 13A socket and created a fire risk.

Don't you mean unfused Dave ?:wink5:
 
Dimplex themselves spec'ed the heater having been provided with my floorplan and room sizes.

Problem is that I actually had a panel in the bedroom before, but thought I would get the Quantum installed as I was getting the other 2 installed anyway, and thought I'd make that extra investment for the longer term saving (my bills were sky high with panels all around!).

So who decided not to install an E7 circuit? I bet that wasn't Dimplex!
 
Ahh - didn't realise the 20A DP switch can't be connected to a ring main, but thinking about it now it kind of makes sense.

The installer obviously doesn't know this however, as they have taken Dimplex's advice as being (in simple terms): where the plug was plugged in via a timer, remove the plug socket, replace with a 20A DP switch, and connect the off-peak element to the new switch.

Then your installer clearly is not an electrician! I would suggest reporting them to trading standards and insisting that they (the installer) pay for an electrician to do the job properly.
 
So who decided not to install an E7 circuit? I bet that wasn't Dimplex!

The decision not to install the E7 (or E10 circuit in my case) was made by the installer. I asked for the installer to come and survey before I parted with any money, as I wanted to understand the route that the new wire going from one end of the flat to the other would take (and if it could be run through the walls).

The installer said that due to studs in the wall as well as the distance, they wouldn't be able to hide the wire in the wall, but would hide it with trunking. He then went on to suggest what I thought at the time was an ingenious idea, and simply connect the heater via a 3 pin plug into an electronic timer, into one of the existing electricity sockets.

Thanks again!
 
The decision not to install the E7 (or E10 circuit in my case) was made by the installer. I asked for the installer to come and survey before I parted with any money, as I wanted to understand the route that the new wire going from one end of the flat to the other would take (and if it could be run through the walls).

The installer said that due to studs in the wall as well as the distance, they wouldn't be able to hide the wire in the wall, but would hide it with trunking. He then went on to suggest what I thought at the time was an ingenious idea, and simply connect the heater via a 3 pin plug into an electronic timer, into one of the existing electricity sockets.

Thanks again!

Presumably you don't have a loft above or floorboards then if they can't run the cable through building voids?
 
Hi All,


Many thanks for all of your help so far. I thought I would post an update considering the installer returned on Tuesday.


p.s. I appreciate that some of the points in my update below may already mention things that you have all kindly advised about already, so I apologise in advance for repetition. I am starting to understand the basics, however am struggling with the exam question of “is it safe or not”?


Since the problem occurred, I have been in frequent email contact with the installer. The installer has also reached out to Dimplex, who have said it would be fine to install the off-peak element of the heater onto a ring main with the usual 32A breaker using a 20A double pole isolator before a 16A timer, assuming that loading, installation, grouping, Volt drop etc was in accordance with BS7671.


The installer therefore came round on Tuesday, and plugged this device into the plug socket which the heater was previously plugged into (before the plug melted). He took a reading of the impedance and explained that the low value means that installing the heater onto the ring main would be fine. Does this satisfy the tests that Dimplex mentioned?


He then proceeded to change the plug socket to a 20A DP switch, and connected it to a 16A timer which was installed beside it. This timer was then connected to the off-peak element.


We left the timer on an “always on” state temporarily to test that everything was working as expected, however after a few hours I noticed that the heater was blowing out cold air. All of the lights were on (on the 20A DP switch, and the timer), indicating that both new outlets were working, therefore I assumed that there was a lose/wrong connection between the timer and the heater. I switched the 20A switch off as I wasn’t going to be at home for a few days.


As you can imagine I was rather frustrated, thus I wrote a rather furious email back to the installer and demanded that these issues are rectified immediately. I also asked for written confirmation that the way in which the heater had been installed was safe and abiding to regulations. I therefore wanted them to accept liability if anything went wrong.


The installer replied and said that they would come and fit a dedicated wire from the fuse box to the room instead, all at their cost. They also said that they would hide the wire in trunking.


Fast forward to this weekend, when I turned the switch and timer back on and also factory reset the heater (I thought that if it was a charge problem, considering that the Quantum detects when it needs to charge and remembers when the electricity to the off-peak element is available and not, the factory reset would do the trick). I was surprised that the heater now worked as expected.


So now I am a bit unsure as to what to do. They have drilled a hole in the plasterboard to install the timer next to the 20A DP switch, so I don’t want a hole left there. At the same time, if there is any risk of danger in using the setup I currently have, I would rather them fit the dedicated wire and live with the annoyance of having a surface mounted wire extending from one end of the flat to the other, on my currently neat, clean and newly painted walls.


Advice would be much appreciated - they are scheduled to return to my flat next Saturday (12th March).



Many thanks in advance!
P.
 
Last edited by a moderator:
In my opinion what they have done is unacceptable, and the fact they have offered to install the correct supply at their own cost suggests that they are aware that what they have done is unacceptable.
I would insist that they make good to all of the holes etc they have made, and route the cable in a manner which you find acceptable.
 
Hello all - hope everybody is having a grand weekend so far!


So I've just had the installers leave (2 of them this time, one who was obviously much more competent and experienced that the chap who attempted to install the heater twice with not much luck).


What they have now suggested, is that the heater in the bedroom is changed from the QM150 (3.3kW) to a QM125 (2.7kW) - obviously at their cost.


The more experienced installer did point out to his colleague that the 20A DP switch should not have been connected to the ring main, as the ring main was protected by a 32A MCB (and therefore the heater was not protected to 16A as it should be).


He said that considering that the current draw for the QM125 would be less than 13A, it would be appropriate, safe and abiding to regulations (he said that electrical testing would pass, should I require this in the future for renting out etc.), for the off-peak element to be connected to a 13A fused spur (connect to the ring main), via a 16A rated timer.


How does this sound to you guys? If you feel that there still needs to be a dedicated circuit, I'll give these guys a call back on Monday and tell them I am not interested in their suggestion.


Many thanks again for all of you that have helped out with this over the past few weeks. It's so impressive and touching that so many people are willing to take a little bit of time out of their day to help me out with this.

Although I am starting to understand the basics, it really does help having you all support my efforts to ensure that the installation is carried out in the correct manner, ultimately leading to me and my family's safety!


Kindest regards,
P
 
My only comment is that the "timer" could be changed and therefore the tenant could use day rate electricity to heat the storage heater.

Is does sound like the installers have improved the situation
 
My only comment is that the "timer" could be changed and therefore the tenant could use day rate electricity to heat the storage heater.

Is does sound like the installers have improved the situation

Many thanks for the speedy reply Murdoch!

Glad to hear that you feel that the situation has been improved - does give me much more comfort.

Agreed that the timer can be changed, however for now I am living at the flat and therefore am aware of how the timer will need to work. Down the line, yes, tenants would need to also understand this (n.b. the main reason I mentioned renting out is due to the fact that I understand electrical testing would need to occur - which I don't want a risk of failing with the setup that they have suggested).

Thanks again,
P
 
Many thanks for the speedy reply Murdoch!

Glad to hear that you feel that the situation has been improved - does give me much more comfort.

Agreed that the timer can be changed, however for now I am living at the flat and therefore am aware of how the timer will need to work. Down the line, yes, tenants would need to also understand this (n.b. the main reason I mentioned renting out is due to the fact that I understand electrical testing would need to occur - which I don't want a risk of failing with the setup that they have suggested).

Thanks again,
P

What certificate(s) have the installers provided?
 

Reply to Dimplex Quantum QM150 Storage Heater Off-Peak Supply Wiring Help in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the...
Replies
3
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
217
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock