Discuss Discrimination on upstairs board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
55
Saw an installation today where an upstairs consumer unit is run off a 40A MCB in the main board.

Two problems

1) Both boards are protected by 30 ma RCD so no discrimination.

2) There's a 40 A MCB in the second board as a dedicated shower feed - the installers have put a 10.8 kw shower on it and of course it keeps tripping the 40A breaker in the main board.

My question is - assuming the cable feeding the secondary consumer is adequate and I feed the upstairs board from on a separate mini consumer unit with a 60A breaker and 30 Ma RCD does that count as a new consumer unit for testing and certification purposes? i.e will I have to sign off on all the upstairs circuits?
 
if you feed the upstairs with a new mini rcd CU you still wont have discrimination with the rcd upstairs.
its just bad design all round to be honest , you need to get rid of the rcd in the upstairs CU.

the shower needs to be on a 10mm cable direct from the downstairs CU
 
If the RCD is taken out of the upstairs unit and replaced with a switch and the whole thing's run off an RCD protected garage unit then that should be discrimination sorted.

Or as the the cable feeding the upstairs unit looks like 10mm MICC perhaps that counts as mechanically protected and doesn't need RCD protection at the origin.
 
or connect the pyro to a 50amp rcbo in the downstairs CU , saves money on a new garage mini CU and gives discrimination to the shower upstairs.
;-)
 
Got any pictures of how pyro should be terminated ? Cos this one don't look too pretty.

Don't think I'll get an RCBO compatible with this board old Wylex MCBs - NB0 - Split RCD - way ahead of its time RCDs labelled BS 4293.
 

Reply to Discrimination on upstairs board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
222
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
666
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
741
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock