Trying to work out how to sort out the mess at a house where the person has numerous air con units, the guy has gone all out and has aircon for each part of the house, He now wants 2 car chargers at 32 amps each. doesn't actually have any 3 phase circuits they are all single phase.
Has 5 socket circuits all at 32 amps. a huge oven that actually only needs a 32 amp but currently has a 50 amp mcb. shower fed from boiler.
What is the diversity for air con units? Was always under impression none is allowed and they are all at 100%?
he has 3 x 32 amp air con circuits a 40 amp air con circuit and a 20 amp air con circuit, if all on that is a huge loading but in real terms might be a lot less.
Thoughts?
 
If you can get to the air con units on the outside, there should be "running current" displayed on the data label, failing that if you get the model No and google the installation doc then you may find running current there. The running current is a fraction of the breaker size, typically a third. Once you have the running current, then its a bit of guess work as to how many will realistically be on at the same time. e.g. bedrooms unlikely to be on at same time as living rooms. In many cases the a/c will be correctly sized and as such the compressor should drop in and out, creating diversity, however, if they are undersized the compressor could run continuously.
Hope this helps
 
Personally I'd just install his car chargers on suitably sized circuits and warn him the the combined load of the oven, the air-con units and the car chargers may cause the main OCPD to trip due to overload if too many items ever run together.

You could load-shed the boiler and a few of the air cons via a current sensing relay and contactor if he's worried about tripping (medical equip in the house maybe) but generally I wouldn't view the main breaker occasionally tripping due to overload as a fault as such. If it happens often enough to be an annoyance he'd simply need to speak to his DNO about upgrading the incoming supply.
 
Don't some of the fancy EV units monitor the total house current and can dial-back the charging if it approaches the DNO fuse size?
 

Reply to Diversity for Air Con units in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
803
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
732
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock