Discuss Diy extension lead 2.5mm twin &earth? in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hi guys I'm needing new extension lead to power light and music centre and have plenty excess 6mm & 2.5mm and 6metres 1.5mm grey twin and earth cable, plugs, sockets and grommets etc. Have basic knowledge of electrics just wanting opinions on using 2.5mm twin and earth cable a new 13 amp plug and fuse and a full metal double socket and back box mounted onto piece of wood for stability the lead will run a straight 5metres along the floor and will supply max 250w. No need for rcd as supply socket is on rcd mcb in cu. But can add 1 if needed? Any opinions?
 
Not usually the standard cable to be used for an extension lead, but it will do the job if you must use it.
Might be a struggle getting the cores into the plug top though.

Go out and buy some proper flex.
 
Not usually the standard cable to be used for an extension lead, but it will do the job if you must use it.
Might be a struggle getting the cores into the plug top though.
It won't do. It's completely the wrong cable and wholly inappropriate for this application. Non-flexible cable isn't suitable for extension leads. Also it cannot be fitted into plugtops. Also plugtops are not designed to accept anything larger than 1.5mm^2. This is non-compliant with BS1363.
 
Every supermarket sells ready made flexible extension leads for a few pounds. Buy one next time you're out grocery shopping.
 
Thanks for all the replies. But why can't this 1.5mm twin and earth be used? as from the socket it will be clipped direct to skirting then the metal back box (secured onto piece of wood) would be screwed direct to the wall just above skirting in the basement the metal faceplate will obviously need earth lead and sheathed. It will never be moved unless being removed all together. Now without all the "buy a lead it's only couple pound"etc remarks can anyone advise me why this is unsafe dangerous etc? Yes I'm bothered saving couple quid and I'm not wasting cash on items that I can make with leftover crap in my lock up. Thanks for any info etc
 
Thanks for all the replies. But why can't this 1.5mm twin and earth be used? as from the socket it will be clipped direct to skirting then the metal back box (secured onto piece of wood) would be screwed direct to the wall just above skirting in the basement the metal faceplate will obviously need earth lead and sheathed. It will never be moved unless being removed all together. Now without all the "buy a lead it's only couple pound"etc remarks can anyone advise me why this is unsafe dangerous etc? Yes I'm bothered saving couple quid and I'm not wasting cash on items that I can make with leftover crap in my lock up. Thanks for any info etc

Please read post #5
 
Gone from home made extension lead to clipped direct possibly becoming radial or spur from existing circuit?? It might work but isnt kosher under the regs.
 
I'm not wasting cash on items that I can make with leftover crap in my lock up.
Send this to your house insurer and ask them to ratify it, in writing, so your cover isn't invalidated in the event of a subsequent fire.

What else do you have in the lockup available for improvisation? Perhaps a length of garden hose and an old watering can nozzle to make a new shower head for the bathroom?
 
Thanks for all the replies. But why can't this 1.5mm twin and earth be used? as from the socket it will be clipped direct to skirting then the metal back box (secured onto piece of wood) would be screwed direct to the wall just above skirting in the basement the metal faceplate will obviously need earth lead and sheathed. It will never be moved unless being removed all together. Now without all the "buy a lead it's only couple pound"etc remarks can anyone advise me why this is unsafe dangerous etc? Yes I'm bothered saving couple quid and I'm not wasting cash on items that I can make with leftover crap in my lock up. Thanks for any info etc
Flat fixed wiring cable like your 1.5mm2 is NOT DESIGNED TO ACT AS A FLEXIBLE EXTENSION LEAD.
 
my crystal ball is telling me the OP isn't listening.......
You're right Mate, met plenty of these stuborn types when I was a box shifter at Electrifix:):rolleyes::D
 
From the IEE code of practice for the In-Service Inspection and Testing of Electrical Equipment:

"Non-flexible cable, such as twin-and-earth, should never be used for connecting an appliance or for an extension lead - the regular bending in use will damage the cable."

I should have thought that was pretty clear.
From the IEE code of practice for the In-Service Inspection and Testing of Electrical Equipment:

"Non-flexible cable, such as twin-and-earth, should never be used for connecting an appliance or for an extension lead - the regular bending in use will damage the cable."

I should have thought that was pretty clear.
Good point Adam, doubt very much if the OP has ever read the ISITEE CoP let alone have a copy.
 
my crystal ball is telling me the OP isn't listening.......

Are you saying the OP intentionally ignored post #5 and when reminded about it he spat his dummy out, sacked off our advice and is currently making the best extension lead ever?????
 
Are you saying the OP intentionally ignored post #5 and when reminded about it he spat his dummy out, sacked off our advice and is currently making the best extension lead ever?????
Reckon you have it nailed Spoon, as for making the best extension lead, could be wrong but I bet he's looking for his dummy.
 
@Yam man you have asked on here regards your plans to supply power to a location. The people who have replied probably equal a couple of centuries experience and knowledge. You do not seem to agree with them! Why? And why even bother asking when you have your own agenda and plans which you are going ahead with in the face of good advice?
 
If the cable and socket were permanently mounted to the wall then this would be no different to any other fixed wiring, but putting a 13a plug on the other end is the issue. As others have stated they are not designed to have solid core t&e terminated into them. And you can't guarantee that the plug won't be pulled out every time you want to use the original socket that it is plugged into, bending the T&E at the same point every time (the first cable clip) until it snaps.
 
Hi guys not spitting dummy out or making lead I work on call been a mechanic recovery. I know that the twin earth cable isn't correct for extension and yes I know yous guys have ALOT more experience etc then me at this voltage I'm used to 12v. So go easy. My plan is to make this as semi permanent as possible the plug will NEVER be removed AT ALL until the day I move or it isn't going to be used again. NO ONE apart from me goes down there as my family don't like my reptile collection. I'm not stupid and have some knowledge of electrics. I have supplied my outbuildings with electric from my cu in house. Also have permanently linked up my lazy spa hottub. I just wanted opinions on why and if this way of extension lead is dangerous. Thanks
 
And as for insurance? I'm in rented property hence why I haven't made it any more permanent. Without been silly guys is there any real danger with my plan all cable will be clipped direct never moved and only carry 300w VERY MAX? not worried bout insurance company they never pay out anyway.
 
Thanks have decided to just use 2.5mm twin earth and just take a 13amp fused spur from that socket and run the cable clipped direct 5 metres to skirting board same as I was going to but instead of a plug on end ill just put it into the rear of the supply socket. Does this sound better?
 
Thanks have decided to just use 2.5mm twin earth and just take a 13amp fused spur from that socket and run the cable clipped direct 5 metres to skirting board same as I was going to but instead of a plug on end ill just put it into the rear of the supply socket. Does this sound better?
You will need to find out if the socket you intend connecting to is on a Ring Final Circuit RFC or a Radial circuit, if it's on a RFC then it will need to be in the ring and not a spur from the ring, if it's a spur then you will need to add a fused spur outlet before you wire to your new socket, suitably fused down of course. It's not just 3 wires is it?
 
Thanks have decided to just use 2.5mm twin earth and just take a 13amp fused spur from that socket and run the cable clipped direct 5 metres to skirting board same as I was going to but instead of a plug on end ill just put it into the rear of the supply socket. Does this sound better?

This is a wind up, or you have a brain the size of a flees --------....
 
And as for insurance? I'm in rented property hence why I haven't made it any more permanent....
... not worried bout insurance company they never pay out anyway.

Hmmm... that sounds like a mature, responsible attitude toward someone else's property that's been entrusted to you.
Perhaps share those thoughts with your landlord?
If any of my tenants took that stance, they'd quickly be homeless.
 
The socket I'm spurring off has 2 sets of twinandearth already in the rear of faceplate that's running from main cu on 32amp mcb that has a 80amp 30ma rcd protection on that curcuit to this socket im going to spur from which leads onto my conservatory sockets etc.
 
The socket I'm spurring off has 2 sets of twinandearth already in the rear of faceplate that's running from main cu on 32amp mcb that has a 80amp 30ma rcd protection on that curcuit to this socket im going to spur from which leads onto my conservatory sockets etc.
That proves nothing.
 
Old boy John Wayne took my horse that's real cowboy. Thanks for all you're sensible suggestions. Decided to just use wife's stocking with sockets on both ends and take notice of members of homeownershub forums who seem to be more helpful rather then criticise now have extension and it hasn't set fire yet
 
I wonder if these pants will suit me...
upload_2018-2-20_15-2-9.png
 
Old boy John Wayne took my horse that's real cowboy. Thanks for all you're sensible suggestions. Decided to just use wife's stocking with sockets on both ends and take notice of members of homeownershub forums who seem to be more helpful rather then criticise now have extension and it hasn't set fire yet
"Yet" being the opperative word. Home owners hub may seem more helpful, but how sure can you be that the info given by said Forum is the correct information?
On a personal note I have given what I consider good electrical advice and information, if you choose to ignore that advice then the onus is on you, you must have realised by now that the advice you have been given, in most parts has been given in good faith, so by all means take advice from others, but be assured that any advice I have given has been correct and unbiased, I wish you luck, and please don't trip over that dodgy extention lead you intend to install.
 
Gone from home made extension lead to clipped direct possibly becoming radial or spur from existing circuit?? It might work but isnt kosher under the regs.
Got to agree with you there the installation method has now changed to a fixed installation.
 
I'm just gutted no one has answered my question in post #40.. :sob:
 

Reply to Diy extension lead 2.5mm twin &earth? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hey, I have a shed in my garden that was built and wired up by my granddad a lonnng time ago and it currently uses 2 core/twin and earth cable...
Replies
2
Views
842
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
876
I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
2K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
My tumble dryer broke, an electrician put a new and stronger capacitor in, couple months later I realised that the socket on the extension lead...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock