Discuss Do Regs allow power socket in an enclosed bathroom vanity unit? in the UK Electrical Forum area at ElectriciansForums.net

rocksolid

DIY
Reaction score
2
I have a socket in by bathroom vanity unit, .75m away from the edge of the bath. The vanity is completely enclosed with a sink on top and doors that, when open, are parallel to the length of the bath.

I hired an electrician to do some work and once he saw the plug in the bathroom, he informed me that he would blank it off, because it is "against the regs." I told him that it's not, because it's in a cabinet. He said, that doesn't matter, it's within 3m of the bath and isn't allowed.

The electrician sent me an "unsatisfactory" EICR due to the socket remaining in the bathroom.

Is the socket allowed in there? Isn't the interior of the vanity unit a separate "location" according to the regs?

What are my options regarding the unsatisfactory EICR?
 
Keeping opinion to one side, your electrician is both right and wrong. Outside of zones, which would be 0.6m from the edge of the bath, certain accessories are permitted. While other accessories and SELV socket outlets are permitted outside of zones, mains voltage socket outlets are not permitted within 2.5m of the boundary of zone 1 (edge of the bath).

The wiring regulations make provision for permanent fixed partitions, but those provisions only affect boundary of zone 2.

No zone exists around basins, but equally no provision is made for vanity units and your basin falls within 2.5m of zone 1 boundary.

As such he incorrectly quoted distances, but would be correct in stating that the outlet shouldn't be where it is.
 
Keeping opinion to one side, your electrician is both right and wrong. Outside of zones, which would be 0.6m from the edge of the bath, certain accessories are permitted. While other accessories and SELV socket outlets are permitted outside of zones, mains voltage socket outlets are not permitted within 2.5m of the boundary of zone 1 (edge of the bath).

The wiring regulations make provision for permanent fixed partitions, but those provisions only affect boundary of zone 2.
Could you point out where in the regs it says that the provisions for fixed partitions only apply to zone 2? 701 .32.1 says:

"Horizontal or inclined ceilings, walls with or without windows, doors, floors and fixed partitions may be taken into account where these effectively limit the extent of locations containing a bath or shower as well as their zones." I see that Fig 701 .1 shows zone 2 being limited by permanent fixed positions, but those are only examples.
No zone exists around basins, but equally no provision is made for vanity units and your basin falls within 2.5m of zone 1 boundary.

As such he incorrectly quoted distances, but would be correct in stating that the outlet shouldn't be where it is.
Yes, the basin/vanity is out of zones (>.6m from edge of bath) and as of the 2022 amendment to the regs, the distance sockets are allowed decreased from 3m to 2.5m. Although vanity units/cupboards/cabinets and similar are not mentioned specifically, they are comprised of fixed partitions and doors which limit the extent of the location containing a bath. If walls, doors and fixed partitions limit the extent of a location containing a bath, why are only some treated as limiting and not others?
 
Could you point out where in the regs it says that the provisions for fixed partitions only apply to zone 2? 701 .32.1 says:

Nowhere. Those are my words as, rather than typing out lengthy passage, it seemed prudent to paraphrase.

"Horizontal or inclined ceilings, walls with or without windows, doors, floors and fixed partitions may be taken into account where these effectively limit the extent of locations containing a bath or shower as well as their zones." I see that Fig 701 .1 shows zone 2 being limited by permanent fixed positions, but those are only examples.

Here you seem to understand the point I was making about fixed partitions affecting the boundary of zone 2. Zone 0 remains unchanged, zone 1 remains unchanged and outside zones is just that. I'm not sure how this could be made clearer.

Yes, the basin/vanity is out of zones (>.6m from edge of bath) and as of the 2022 amendment to the regs, the distance sockets are allowed decreased from 3m to 2.5m. Although vanity units/cupboards/cabinets and similar are not mentioned specifically, they are comprised of fixed partitions and doors which limit the extent of the location containing a bath. If walls, doors and fixed partitions limit the extent of a location containing a bath, why are only some treated as limiting and not others?

Specific mention is made of airing cupboards and the door through which one enters and exits the room. I'm fairly certain that the IET members who draft wiring regulations will be aware of the existence of vanity units, but for reasons known only to themselves have not seen fit to classify these in the same category as an airing cupboard or bathroom door.

Using my google-fu, I also came across these two forums, which describe the same situation - socket in the bathroom, enclosed by partitions via airing cupboard/cabinet. There are at least 4 people saying that this is ok and is a "no code" situation.

Power socket in bathroom

Socket in airing cupboard

Four people said this was okay. Who were these four people and what qualified their opinion? How many others were of a different opinion?

You asked a question and I answered it. I'm sorry if the answers weren't to your liking, but such is life. The electrician you contracted to carry out the EICR has inspected the property and reported on it as they saw fit. I very much doubt you're going to sway their opinion, so the options are accept their opinions or have someone else carry out another report and hope they see this matter from a different perspective.

There are different means of achieving the same ends and having a socket under a bathroom washbasin doesn't seem to me to be a hill worth dying on.
 
Could you point out where in the regs it says that the provisions for fixed partitions only apply to zone 2?

Somewhere towards the beginning of the regulations are the requirements to use good workmanship, proper materials, good engineering judgement etc etc.

Basically it boils down to common sense, electricity is dangerous, electricity mixed with water is very dangerous, don't create a situation where they could end up mixed.
 
Nowhere. Those are my words as, rather than typing out lengthy passage, it seemed prudent to paraphrase.



Here you seem to understand the point I was making about fixed partitions affecting the boundary of zone 2. Zone 0 remains unchanged, zone 1 remains unchanged and outside zones is just that. I'm not sure how this could be made clearer.



Specific mention is made of airing cupboards and the door through which one enters and exits the room. I'm fairly certain that the IET members who draft wiring regulations will be aware of the existence of vanity units, but for reasons known only to themselves have not seen fit to classify these in the same category as an airing cupboard or bathroom door.



Four people said this was okay. Who were these four people and what qualified their opinion? How many others were of a different opinion?

You asked a question and I answered it. I'm sorry if the answers weren't to your liking, but such is life. The electrician you contracted to carry out the EICR has inspected the property and reported on it as they saw fit. I very much doubt you're going to sway their opinion, so the options are accept their opinions or have someone else carry out another report and hope they see this matter from a different perspective.

There are different means of achieving the same ends and having a socket under a bathroom washbasin doesn't seem to me to be a hill worth dying on.

Thank you for your contribution.
 

Reply to Do Regs allow power socket in an enclosed bathroom vanity unit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone! You all seem like a friendly bunch and google keeps referring me back to here but I still cannot find any solid answers so...
Replies
20
Views
3K
So this was an interesting conversation today and wanted peoples advice. Plumber asked me if I could fit a socket inside an enSuite Vainty unit...
Replies
21
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
My first posting and hope you guys can help. I am a householder in the process of planning a refurb of our bathroom (not DIY) and putting together...
Replies
11
Views
3K
Hi all, I think I'm posting this in the right place - apologies if not. I'm wondering if I could ask for a bit of help here. I'm renovating a...
Replies
32
Views
17K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock