Not exactly, but you can get the add on vigi units from Eaton I believe, with a time delay, that turn your 60898 into a 61009. You can also get circuit breakers with adjustable time delay RCD settings but these fall into the 947 standards. These are switchgear components, high end, and cost thousands, but I'm guessing neither of these are what you're after? :D
 
As DS indicated it's only possible using S type add on Viggi units, but that will take up 4 spaces on a typical single phase CU/DB. Plus you could have the common buss bar conflict with the neutral connection.
Other than that, i've not seen or know of a time delayed RCBO.
 
Separate S type and an MCB alongside.
 
As above

How many modules do u have spare/ how many poles do you need

Hager do a add on unit now too like the Schneider Viggi. Control gear direct also do 2 & 4 pole rcbos not to sure if they come in s type, download the cat from there website
 
Last edited:
There's usually no call for a time delayed RCBO set-up If your following the BS7671 which brings me to question what circumstances require you to need a time delayed RCBO as this would not comply for protection of a circuit be it from shock hazard or buried cable protection.
 

Reply to Do time delayed rcbo's exist? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to put a code pad via a time delay relay on a shutter door, any recommendations?
Replies
7
Views
588
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
4
Views
163
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
759
Hello everyone, Is it necessary to test RCBO x5? Some say that you can’t even test at x5 times because it can damage RCBO. Others that you can...
Replies
4
Views
896
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock