situ is a park homes prefab for sale. i have been tasked with doing an EICR. wylex 3036 board with a later added 30mA up front RCD. Ze = 0.3. Zs readings at cooker outlet 0.32. lights 0.47. RFC sockets all read between 687 and 720 ohms. cpcs are intact and connections checked. tested the Zs on both sides of the RCD to eliminate bogus readings there. 1553 aborted RCD test showing >50V. obvious conclusion is a floating earth, but no visible signs of a fault. going back tomorrow with wander lead to check some R2 readings. just to eliminate test faults, got home and plugged 1553 into a socket. 0.47 ohms on hi current. 0.47 ohms on no trip. any ideas?
 
I'd be tempted to split the rfc where you think the halfway point is, and then measure the resistance of the 6 legs back to the board with your wander lead. Then see if there's any unexpected values or cross connection.
I know it sounds simple but going back to basics has helped me out many times when I can't understand what's happening?


Sent from my GT-I9505 using Tapatalk
 
Are you certain there isn't a socket or FCU on the ring that you may have missed Tel ? It sounds like nothing more than a loose connection somewhere to me ? [Unless there's a dodgy junction box or similar underneath ?]
 
going back tomorrow with a wander lead. get the r1, r2, rN readings, then wander the R2 to a socket. 1 socket is only about 4ft. from the CU. so that. a starter.
 
All continuities OK, tel?
going to test them tomorrow. had not got wander lead today and was a bit rushed as we have the kitchen fitters in today .
 
Sorry, just noticed previous post. If it's affecting all sockets, thus both ring legs, it seems the problem is close to the circuit origin.
Float on, I say.
 
update. went back dead tests all OK. r1, r2, rN, R1+R2 , all well as expected. reconnected in CU and did a hi-current test at CU with L-E shorted at approx mid-point. Zs then came in at 1.5 ohms. considering the Zdb was 0.8 ohms, not a bad reading.
 

Reply to doing my head in. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
Favour for a mate has turned into a nightmare. Really appreciate any comments on the below! Was asked to look at some sockets which have...
Replies
8
Views
4K
Hello Over the last 2 weeks I have been doing some electrical work for the neighbour of my Daughter as they had been let down by 2 other...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top