I sorry to side step your question here but the cable has to be glanded correctly regardless of how you found it, if you do any work on the sub-mains you take on the responsibility for the safety and condition of the existing supply to the submains, it may be buried but you cant predict issues like, subsidence, chemicals in the ground, inherent fault with the cable and any or other issues could create a fault down to the armour and if you havent correctly terminated it it could make the armour live without operating a protective device.
If you are in a situation as you say and truely can't gland it then i would suggest you cut a ring section of outer sheath away and fit a DNO style cable sheath earthing clamp (not a bonding clip!), then i would seal it with plenty wraps of amalgaming tape, this cable armouring must be earth at the supply regardless of the limited risks you perceive. Also because it has no rigid fixing to the dist' board you need to ensure the cable is fully supported and cannot be physically moved this way no movement will stop the termination from working loose.
In answer to your question the 35mm as you have realised is under sized and i would say no rodding the local ground, IMHO this isnt a solution and you will find it hard to prove compliance although others may suggest otherwise for which im open to discussion, rodding is really for TT where its your only option regarding earthing and a few other situations where you cannot export the earth but when your installation has a full earth provided system and you are not exporting it then you should be using the earthing provided.
I know you have probably looked over this time and time again but is it really impossible to fit a gland as this seems hard to believe or is it just really arkward and inconvenient.
I also drag up the correct glanding issue because if you can manage it then all your worries are solved regarding compliance.