Means even if the Zs value is higher than values mentioned in the BS7671 Table, the RCD will disconnect the earth fault . Am I wrong?

The RCD will disconnect quickly at impedances well above the Zs needed for the MCB, so in that sense you are right.

But equally if the Zs values is higher than what was designed (or reasonably expected for the type of circuit and size of installation) then it points to something going bad. Could be a loose joint, cable near the point of fracturing, bad repair with seriously under-spec cable, etc, which should be investigated.
 
So practically, if there is any earth fault, the RCD would detect and remove the fault much quicker than MCB
Yes, practically

BUT

an RCD is only an additional protection device. The circuit should be designed so that an MCB/fuse will disconnect the supply in the event of an earth fault. So the circuit must correctly meet the EFLI criterea.
 
an RCD is only an additional protection device.

This is a very important point.

An RCD (and the equivalent section in an RCBO) is an order of magnitude more complicated than a MCB and far more likely to fail "unsafe", hence the periodic testing that is specified (though I doubt most folk do it).
 

Reply to Earth Fault Loop Impedance Test for lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
419
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
702
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
576
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
750

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock