Discuss Earth Leakage Relay connection with normal CT in the UK Electrical Forum area at ElectriciansForums.net

No it should be CBCT. When there is no fault the output is zero, when a fault is detected this breaks the balance. All conductors pass through a CBCT, this is how it functions a CT generally only encompasses one conductor giving constant output to the CT when under load.
 
Can I use normal CT with Earth Fault Relay ? Like DELAB Earth Fault Relay (EFR).

Normal CT I’m using here it’s CT used with Amp meter or Over Current Relay (OCR). So is there any other name instead of normal CT?
 
You would have to speak with Delab, earth leakage relays normally function by CBCTs but with new technology who knows whether a CT would suit.
 
A CBCT is essentially a toroidal transformer, all conductors for the circuit pass through but not the earth. When no fault is present the vector sum of currents is null but when any earth leakage occurs the balance is broken and this is measured in the toroid giving secondary output to the leakage relay.
A CT transformer produces secondary output which is proportional to the primary and hence while the circuit being monitored is using current there is always secondary output. This can be used for overcurrent protective relays and whilst I am not 100% certain I do not think this will suit a leakage relay.
I am sure Delab will give much better advice than myself.
 
Hi,
DELAB Earth Fault Relay (EFR) can connect with DELAB Over Current Relay (OCR), see the picture.. so, it means it’s connected using Normal CT? Right? But I know DELAB have there own CBCT for there ELR. My question is what is different between EFR and ELR? How is it functioning EFR using normal CT?

26A72FE2-1D54-4EDA-B14E-22FCECF05A61.jpeg
 
A CTs output is dictated by how it is wound but that is showing an earth fault relay which may not be the same for an earth leakage relay.
 
I have just been looking online for the earth fault and earth leakage relays from Delab. Wiring diagrams differ as it shows a CBCT for the leakage relay and CTs for the fault relay.
 
I’m posting this question because, one of my friend are studying Electrical program. There instructor saying CBCT will create using 4Nos of Normal CT. I’m also not believing this. That’s why I’m discussing. I think DELAB EFR will not working using CBCT. Only ELR will work. I’m right? And also DELAB ELR will not working using normal C.T. I’m right? What’s your idea?
Thanks
 
CTs can be used for overcurrent and fault relays but a CBCT is used for a leakage relay but never say never. If you used CTs for a leakage relays to me it will be constantly tripping, a CBCT doesn't give an output when no leakage is present.
 

Reply to Earth Leakage Relay connection with normal CT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
388
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
596
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock