No it should be CBCT. When there is no fault the output is zero, when a fault is detected this breaks the balance. All conductors pass through a CBCT, this is how it functions a CT generally only encompasses one conductor giving constant output to the CT when under load.
 
Can I use normal CT with Earth Fault Relay ? Like DELAB Earth Fault Relay (EFR).

Normal CT I’m using here it’s CT used with Amp meter or Over Current Relay (OCR). So is there any other name instead of normal CT?
 
You would have to speak with Delab, earth leakage relays normally function by CBCTs but with new technology who knows whether a CT would suit.
 
A CBCT is essentially a toroidal transformer, all conductors for the circuit pass through but not the earth. When no fault is present the vector sum of currents is null but when any earth leakage occurs the balance is broken and this is measured in the toroid giving secondary output to the leakage relay.
A CT transformer produces secondary output which is proportional to the primary and hence while the circuit being monitored is using current there is always secondary output. This can be used for overcurrent protective relays and whilst I am not 100% certain I do not think this will suit a leakage relay.
I am sure Delab will give much better advice than myself.
 
Hi,
DELAB Earth Fault Relay (EFR) can connect with DELAB Over Current Relay (OCR), see the picture.. so, it means it’s connected using Normal CT? Right? But I know DELAB have there own CBCT for there ELR. My question is what is different between EFR and ELR? How is it functioning EFR using normal CT?

26A72FE2-1D54-4EDA-B14E-22FCECF05A61.jpeg
 
A CTs output is dictated by how it is wound but that is showing an earth fault relay which may not be the same for an earth leakage relay.
 

Reply to Earth Leakage Relay connection with normal CT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
419
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
523
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
622
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock