Search the forum,

Discuss Earth Leakage Relay connection with normal CT in the UK Electrical Forum area at ElectriciansForums.net

I have just been looking online for the earth fault and earth leakage relays from Delab. Wiring diagrams differ as it shows a CBCT for the leakage relay and CTs for the fault relay.
 
I’m posting this question because, one of my friend are studying Electrical program. There instructor saying CBCT will create using 4Nos of Normal CT. I’m also not believing this. That’s why I’m discussing. I think DELAB EFR will not working using CBCT. Only ELR will work. I’m right? And also DELAB ELR will not working using normal C.T. I’m right? What’s your idea?
Thanks
 
CTs can be used for overcurrent and fault relays but a CBCT is used for a leakage relay but never say never. If you used CTs for a leakage relays to me it will be constantly tripping, a CBCT doesn't give an output when no leakage is present.
 

Reply to Earth Leakage Relay connection with normal CT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all Suggestions please. I’m working on a 3 phase shop install with a bunch of typical circuits. As each cct is energised the earth leakage...
Replies
6
Views
437
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
625
Hi I currently on a job where the garage is having an office built above it with solar panels installed on the roof. I have ran a 16mm 3 core...
Replies
3
Views
186
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top