Discuss Earth plug burnt? in the UK Electrical Forum area at ElectriciansForums.net

Martiv

DIY
Reaction score
1
Hey there im running an extension to my shop/shed heavy duty rated it powers 2x 400watt hallogens which i use in my chicken brooders
There on a timer so they come on at normal day time and at night time it swaps to 2 red heatlamps.

My bulb was making a whistle noise normally means replace it. So i did. Then i see the timer on the earth has brown marks on it melted plastic slightly..

I checked my lights and there transformers there all new and working for last year under 5year guarantee but i back traces it to the wall and i saw the plug socket at the wall has a crack through the socket hairline bit its cracked through the 3 holes.

Could this be why my timer further up the line has burbt on the earth?

I checked rarings and i am safe i run 4amp on a 1.5mm 13amp heavy duty work cable which goes toa heavy duty contactor timer then to my lights if anything over safe apparently cause it could tske somuch more

Ive moved the babys into a makeshift brooder in the house but il have another 30 eggs hatching any day..


I will change the plug socket of course.
And the timer.

But i want to know if this crack would be the cause of the timer burning on the earth terminal 14 meters down the extension?
And if so why didnt the plug burn but the timer?

I want to know if this is the problem anf why and how so i can learn.
And i want to know if i change the plug socket if i am then safe to continue and basicly that my lighting units will be safe ive no idea how i isolate this issue without knowledge

I csnt afford an electrician to come out at the moment i am skint but chicks need heat
 
If the earth terminal is burned then that is a sign that you may have a serious and potentially very dangerous problem.
In normal use there should be no current flowing in the earth, if it has indeed got hot and burned then it has current flowing through it.

You need to isolate all of the equipment that was plugged in to that socket and not use that socket until you can get this checked by a professional.
 
Out of interest how many chicks and why not use a proprietary brooder? 800W sounds a lot, are you warming them or doing your own KFC?
 
Perhaps the heat is tracking from the live or neutral and only showing at the earth from the outside? Look inside the the socket, with the power off of course, and see if theres any damaged cabling there.

As mentioned, the earth should not carry any current normally... only if there's a fault

Maybe a forum member could help if local to you. You only have UK as your location.
 
Post some good quality pics of the damaged items. Burnt parts such as plug pins are usually caused by localised bad contact e.g. within the plug or the socket it's plugged into, rather than any remote factors. However, a burnt earth connection is very unusual and could signify a problem elsewhere, including a serious one as Davesparks says.

My hunch is that the burn on the timer was caused by an overheated part inside that has nothing to do with the earth connection, it's just nearby, and even less to do with the cracked socket outlet. But it's all speculation until we see pictures.

Oops, post crossed with PC1966
 
Out of interest how many chicks and why not use a proprietary brooder? 800W sounds a lot, are you warming them or doing your own KFC?
Its a 350w infra red and a 400watt chick brooder lamp apparently with a vitamin release.
There normaly in the shed which csn get to 5degree and colder in winter. Chicks need 35 degree and drop by 5 each week. Or they die so to stop any heat drop we run these through the night we had 250watt but they didnt heat it up enough so instead of using 2 at 500watt we got 1 400 lol.
The infra red light couldnt find in 400 but 350 is working nice. We have 30 to hatch this time round and another 200 to bring over the nex weeks not alot but want it perfect of course.



The pics looks fine to me i cant see any burn inside the timer its at the edge of the plastic...?

Ill get pics in the socket soon as i turn the power off
Later kids gona go nuts without the internet lol
 

Attachments

  • 20200527_134706.jpg
    62.9 KB · Views: 62
  • 20200527_134652.jpg
    77.9 KB · Views: 63
  • 20200527_134404.jpg
    90.8 KB · Views: 58
  • 20200527_134356.jpg
    104.7 KB · Views: 56
  • 20200525_221909.jpg
    50.3 KB · Views: 58
Last edited:
Am I supposed to be seeing something burnt? I can see some tiny discolouration to the plastic near the earth aperture but it's not caused by the pin overheating, otherwise it would be only be brown where in contact with the metal. Maybe I'm missing something.
 
Can I just ask, are the lamps/heaters metallic and fixed to any metal going into the ground, such as the metal fabric of the shed, or stands in contact with the ground, or water pipes, - basically any connection between the earth from the socket outlet/plug and the earth in or near the shed in any way?
 
We need to see a picture of the burned earth connection.

All I can see from that is a bit of dirt near the earth socket and what looks to be a timer made by Fisher price.
Im uploading pics soon. Sorry for the wait ive baught a plug tester with 14 wire configs by megga. Wanted to test broken socket to get a reading first. I pick it up at 9. Baught the new socket 2gang 13amp too. And new metal box plate


Timer was off amazon says its a heavy duty contactor for lighting and stuff with really good reviews by lumii they make them for greenhouses ponds etc so thaught it would be good it was only ten wuid.
I got then from advice as i had cheap bnq timers.
Told they can burn out.

Got 4 chicks hatch today lol kids wont leave their sides
 
Please post pictures of the damaged plug, outside and inside showing the connections (unless it's a moulded plug that can't be opened.) Otherwise we don't know what kind of problem we're discussing, if any.
 
Havong phpne problems sorry im late..
Its a heavy duty infra red 350watt brooder
And a poultry green 400watt sodium supliment lamp which goes on a ballast. The infra red heats more somehow lol. They dont cook lol at 3ft i getv35 degree in the brooder and it keeps the roost warm same time without using heat bads and bulbs in there. The hens. Like to smash about and damage lights in there anywho lol.


Anyways on to the problem
I got my soket testwr which says the socket is fine.
I dont like how dirty it is. I am about to put a 2pole in and as u can see earth is in a single jacket.. Am i right in thinking i dont need to but its better to reshrink 3.mm each and use both poles?

Now the plug that was in the timer from ballasted light. Where the plastic is is where the brown was mirroring the brown from the timers plastic.


Timer says all works too.. And has no damage internally?
[automerge]1590692255[/automerge]
Been a hot day my daughter spending all her time with the chicks at the moment warmer outside than in the shed at the moment night time there in my house the lids want them to stay there hahahaScreenshot_20200528-194126_Messenger.jpgScreenshot_20200528-194056_Messenger.jpg20200528_175716.jpg20200525_221909.jpg20200528_100453.jpg
 

Attachments

  • Screenshot_20200528-194220_Messenger.jpg
    41.1 KB · Views: 23
  • Screenshot_20200528-194216_Messenger.jpg
    38.3 KB · Views: 23
  • Screenshot_20200528-194210_Messenger.jpg
    26.5 KB · Views: 24
  • Screenshot_20200528-194208_Messenger.jpg
    42.2 KB · Views: 24
  • Screenshot_20200528-194204_Messenger.jpg
    47 KB · Views: 24
  • Screenshot_20200528-194201_Messenger.jpg
    55.2 KB · Views: 24
  • Screenshot_20200528-194201_Messenger.jpg
    55.2 KB · Views: 24
  • Screenshot_20200528-194152_Messenger.jpg
    44.8 KB · Views: 24
  • Screenshot_20200528-194141_Messenger.jpg
    81.2 KB · Views: 25
  • Screenshot_20200528-194137_Messenger.jpg
    52.3 KB · Views: 23
  • 20200528_195632.jpg
    107.7 KB · Views: 23
Last edited:
In my opinion that's a bit of dirt, or maybe a fly or insect, that has got trapped between the plug and the socket, not any kind of burn or overheating mark.

The socket is cracked, just swap it out for a new one and carry on.
 
In my opinion that's a bit of dirt, or maybe a fly or insect, that has got trapped between the plug and the socket, not any kind of burn or overheating mark.

The socket is cracked, just swap it out for a new one and carry on.
I thaught so too but didn't wana say myself.
Thankyou somuch you guys saved me somuch.

Have more questions coming soon hehe as il be making a bandsaw shortly too hehe
[automerge]1590698442[/automerge]
As per the earth socket 2 pole..

Do i seperate the double ewrth and re sleve them to both poles?

So leave doubled in 1 and run a little wire in the other to metal case? Dont see what that does but manual looks like that?
[automerge]1590698560[/automerge]
 

Attachments

  • 20200528_214201.jpg
    79.6 KB · Views: 15
  • Screenshot_20200528-194201_Messenger.jpg
    55.2 KB · Views: 16
Do i seperate the double ewrth and re sleve them to both poles?

So leave doubled in 1 and run a little wire in the other to metal case? Dont see what that does but manual looks like that?

Connect it exactly as the old one is, reds to live, blacks to neutral, both earth's to one of the earth terminals.

An earth link to the back box is not strictly required but a lot of us would consider it best practice to fit it.
 

Reply to Earth plug burnt? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K
I’m welding and have a cable blue 2.5mm 3 core 10metwrs to reach my shed the plug and socket I got to wire on them biggest hardware has says...
Replies
11
Views
4K
Sorry two questions today. We had the kitchen rewired based on existing units, but with a slightly new layout it puts the dishwasher right over...
Replies
1
Views
706
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock