Discuss Earth to neutral fault???? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi, I have an old style fusebox and planning to replace (via electrician) with a modern one (wiring was uprgaded by previous owner) and I noticed when removing a spur line to the outside that was not going to pass muster that my multimeter was showing that earth and neutral were connected. I checked some other sockets and lights, same thing, which I guess you would expect as neutral wires are attached to the same plate in the fusebox. When I switched the fusebox off the connection between earth and neutral disappeared so the problem seems either in the fusebox or just the mains supply, as I believe neutral and earth are somehow bonded on some systems? Just wondering if I have a problem or not? House was built in 1955.
 
When you turn the main switch off it disconnects the live and neutral conductors.

On a TN earth system the earth and neutral are joined before the switch on the suppliers side.
 
But I am still testing the same neutral and earth circuit even with the box turned off so if the fault disappears does it not mean it is in the fusebox or just the mains earth/neutral bond showing up when switched back on
 
Hi, sorry but it would be a bit brave to say there isn’t a fault. The test equipment is not what is normally used and it’s not really possible for us to confirm how you have used it. What you have is a possible explanation for what you are reporting, if that makes any sense.
BA7AADC6-C92B-4702-9F26-4C1F56325BB1.jpeg
 
As mentioned above, earth and neutral are solidly connected at the source of supply in all public supply systems, and may in fact be the same conductor part or all of the way from there to your house.

On TN systems there will only be a fraction of an ohm of copper between your consumer unit and the connection. If it is TN-C-S that will be a very small fraction indeed because there will be a solid connection within your own service head. On a TT installation with the earth obtained via a rod / electrode, there might be a hundred ohms or more between earth and neutral at your end, but the connection is just as solid at the supply end.

The connection at source keeps the neutral near earth potential and is what makes it a neutral (as far as single-phase installations are concerned.) The other wire, the one that is not connected to earth, then becomes the line.

If the continuity disappears when you turn off the main switch, there is no indication that your installation is faulty, this is what you would expect. However, despite being near earth potential, neutral is considered a live conductor (it is part of the energy supply circuit) and you should not go poking around at it with the continuity tester with the main switch on. In any case, whatever reading you get is somewhat arbitrary because there is usually some AC voltage present (due to voltage drop along conductors) and most continuity and resistance tests are not supposed to be carried out with stray voltages present.
 
Last edited:
Thanks for the illustration, it does not have the electricity co isolator switch but the earthing looks about right and all the neutral wires come off the same terminal in the fusebox, worried it is going to trip the new fusebox, although have not had any problems with the current wiring.
 
What we can say is that with the main switch on, with the 2 most common earthing systems in urban areas you can expect to see continuity between earth and neutral.
The diagram above from @Wilko showed TN-C-S which is the most popular for new installs and what many others are slowly being converted to (I won't get into a rant about this). It would be a reasonable bet you have this system if you don't live in the middle of nowhere. On this system the Earth starts at the Neutral at your supply, hence the link.

The fact you lose continuity with the main switch off further supports the likelihood that this is what you are picking up.

So at this point, no definite fault. The electrician will check all of this stuff with a more sensitive testing device before he starts so I wouldn't be concerned.
 
Thanks for the illustration, it does not have the electricity co isolator switch but the earthing looks about right and all the neutral wires come off the same terminal in the fusebox, worried it is going to trip the new fusebox, although have not had any problems with the current wiring.
Ahead of any consume unit change, especially if going from old to new, the electrician will conduct some tests with a much more sophisticated test instrument to minimise this risk. The idea is that before he starts tearing everything out he makes sure that it's going to work afterwards!
Having checked the fixed wiring is ok, the other possibility that can cause issues afterwards is fixed equipment, e.g. immersion heaters, cookers, showers, as sometimes they still work but the elements have deteriorated enough to cause a little earth leakage. In this situation the new consumer units notice that some electricity is going the wrong way and will disconnect the supply out of concern it's going through you! This is comparatively rare though.
Hope that helps.
 
Here are some diagrams showing the 3 commonly used earthing systems in the UK, shamelessly stolen from the "IET Wiring Matters | Autumn 11" article elsewhere. Here PE = "protective earth" and PEN = "protective earth neutral" and the 'T' part in the designation comes from 'terre', the French for earth.
TN-S-earth.png

TN-C-S-earth.png

TT-earth.png
 
Last edited:
It was in some other article that Lucian pointed out it is the connection somewhere between the Earth and one of the current-carrying conductors that defines it as neutral.

So when energised you would expect to see a low resistance between N & E, but that should always be on the supply side of the installation. It is not permitted to have N & E common in an installation in the UK (known as a TN-C supply, seen in some older European places) and for any RCD device it would see that as a fault.

So ultimately you are right that the N & E needs to be checked for insulation quality as part of an upgrade, just as L & E/N needs checking, but that would be done by any competent electrician before energising the modified system at 250V or 500V DC to be sure all is OK.
 
For interest only (earth to neutral fault), I have a 1972 install still with the old fuse box install, a 30 ma RCD was installed many years ago with whole house protection and worked perfectly for years without any nuisance tripping. A 9 kw shower is separately protected with a 40A/30ma RCBO. One day, about 10 years ago the RCD kept tripping for approx 3 hours, I found a full E to N fault, ("0" ohms with a multimeter), the shower still had power (as expected) during this period. After 3 hours the fault disappeared, never again to return, I often think about this as I really did nothing to track it down. My system is TNCS.
 
Last edited:
One day, about 10 years ago the RCD kept tripping for approx 3 hours, I found a full E to N fault, ("0" ohms with a multimeter),
To be honest I think this might be a case of 2+2=5
You had an Earth leakage fault for 3 hours, and during that time you measured 0 ohms between neutral and earth.
If you repeat the measurement today with the same meter you will still find the 0 ohms as Neutral is joined to earth in the suppliers cutout. A more sensitive test instrument would show that there is resistance present of fractions of an ohm.
I think this measurement was a red herring regarding the temporary fault.
 
I still figure that 2+2=4 Tim, when my double pole RCD is tripped and with a healthy system I get infinity between N & E (my side) and I get a very very small resistance when the RCD is closed (practically 0) . I just checked it out there now. When I had the fault I was getting practically 0 resistance with the RCD tripped and I couldn't reset it until it went to infinity.
 
I still figure that 2+2=4 Tim, when my double pole RCD is tripped and with a healthy system I get infinity between N & E (my side) and I get a very very small resistance when the RCD is closed (practically 0) . I just checked it out there now. When I had the fault I was getting practically 0 resistance with the RCD tripped and I couldn't reset it until it went to infinity.
My apologies, yes, I see you meant on the load side of the rcd now.
 
By definition , If N gets joined to E after an RCD it will trip.

( without a diagram of what has been ruled out .. we all get confused !)
..detecting small AC voltages present on Earthed things ..can upset some simple
OHMS measurements.
Hence the interest in low current AC clamp meters.
 
Last edited:
It will, but only if there's a L to E fault (leakage) or a N to E fault on the consumer side?. I was getting a full short between N & E with RCD tripped at different periods for ~ 3 hours, the mystery is why it was coming and going and then disappeared "for ever".
 
Last edited:

Reply to Earth to neutral fault???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
541
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hi all. Reasonably competant non electrical engineer homeowner here. I have a question for the experts: I recently replaced a horrible...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock