Discuss Earthing System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

depends on what the other end of that EC is connected to at t'other end of the duct.
 
True it could be TNCS...
Unfortunately I won't be able to find out where the other end goes..
Ze reading is 0.19 Ohms, isn't very low as for tt system?
 
True it could be TNCS...
Unfortunately I won't be able to find out where the other end goes..
Ze reading is 0.19 Ohms, isn't very low as for tt system?
It's not likely to be TT at 0.19 Ohms (never seen that low a value). If the L-N impedance is higher than Ze then I'm voting with Karin and Spary for TNCS. Is there a prize for the correct answer ? :)
 
Well it's 0.16 Ohms.. What now?
A lollypop as a reward hehe
Is it true that if impedance between L-E is the same as between L-N then it's a TNCS?
 
There used to be a requirement to stake PME systems to keep the resistance to earth below 20 ohms maybe that is what it is?
 
If it is in a block then that earthing stud could well be doubling up as the Building Network Operators earth marshalling point and the conductor rising from the duct could be a main protective bond of the incoming water / gas / steel (although this does look potentially a bit undersized).
I would be contacting the DNO to ask what the earthing system is and what the size of the supply is so that you are able to confirm adequacy of the bonding in relation to the supply neutral
 
Thanks guys for all your help, much appreciated.
I phoned the ukpowernetworks (London area) and they said they don't have this information... something is not right.
I'll call them again on Tuesday.

Thanks again and enjoy your weekend!
 
Tony i must be blind then..Where did you find it, could you send the link? I would appreciate it

Thanks again guys for your help, problem solved
 

Reply to Earthing System in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing...
Replies
9
Views
635
Hi do tt earth systems highly require a rcd, and if not are upfront rcds a must in the tt earthing systems? Cheers
Replies
27
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Is blue neutral or earth when there is a black cable (which is the old neutral) - old system? Other one is red, no green / yellow
Replies
6
Views
335

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock