Discuss Earthing Systems in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
44
Can anyone confirm this Earthing system please.

11KVA line to transformer.
Off the transformer line to 1 cable to house
Off other side of transformer to earth rod and 2nd line to house
At house outside. Transfers to DNO equivalent of 1 core swa with core connected to line and armour connected to 2nd cable. Also off 2nd cable is another single line going to MET in house.
DNO SWA goes to cutout as normal.

I first thought TNS from in the house due to seperate earth but now thinking PME.
I'm calling DNO tomorrow to confirm what it is
 
If the earth is provided separately from the incoming neutral then this is a TNS supply at the house.
It is entirely possible that the supply cable is multiply earthed along it's route but this is not something about which we can speculate as we can only operate based on the incoming supply cable to the cutout.
If the arrangement is that the neutral and earth have been combined by the DNO at the outside of the house and then only fed a neutral and line into the house and split off the earth to the MET at the service head then this would be (from our point of view) TNCS.
 

Reply to Earthing Systems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
749
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
536
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
582
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock