Discuss Economy 7 to 24hr supply. in the DIY Electrical Advice area at ElectriciansForums.net

JohnAli

DIY
Reaction score
0
Is it possible to change the supply to Storage Heater sockets from Economy 7 to normal 24hr supply?
Have disposed of the old storage heaters and need the supply changed so I can use "normal" heaters.
However I do not want to get rid of Economy 7 fully as I have an Immersion Heater and a large Storage Heater with blower that I would like to keep on Economy 7.
Is this feasible?
Do I just need an Electrician to change the wiring at the consumer unit to 24hr supply?
Cheers, John.
 
It's certainly possible to change the supply to the E7 consumer unit to a 24 hour supply, but things are complicated by the remaining storage heater and the water heating.
There are a few ways to solve this. The cables to the discarded storage heater points could be moved to the existing 24 hour CU, if there's enough spare wire to do this, and sufficient space in the CU to accommodate new circuits (doesn't need one spare way for every circuit). The two E7 circuits that are still required can be connected to a small new CU, fed by the existing E7 tails, or the water heater and storage heater can be fitted with individual time switches.
If not already, the new socket circuits will need RCD protection.
 
It's certainly possible to change the supply to the E7 consumer unit to a 24 hour supply, but things are complicated by the remaining storage heater and the water heating.
There are a few ways to solve this. The cables to the discarded storage heater points could be moved to the existing 24 hour CU, if there's enough spare wire to do this, and sufficient space in the CU to accommodate new circuits (doesn't need one spare way for every circuit). The two E7 circuits that are still required can be connected to a small new CU, fed by the existing E7 tails, or the water heater and storage heater can be fitted with individual time switches.
If not already, the new socket circuits will need RCD protection.
Thank you, much appreciated!
 

Reply to Economy 7 to 24hr supply. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
576
Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Long story short im on economy 7 tariff but have 2 types of heaters in my house 1 convector fused socket, 3 storage heaters not fused sockets. So...
Replies
1
Views
770
Good day readers, if any,I am an old sparky, a very old sparky. I can remember old Faraday giving us lectures Wednesday evenings at evening...
Replies
1
Views
406

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock