Discuss EICR 1 bed flat- simples in the UK Electrical Forum area at ElectriciansForums.net

O

ohmslow86

Hi,

scenario is. TNC-S 100A BS1361 main fuse at DNO cutout. 16mm tails feeding meter. 2x 16mm T&E cables coming out of meter (no switch fuse) going through wall (un-protected) up cavity across attic to the House DB and storage heating DB-both 15m away. Ze-0.17 pfc-1.32

The 6mm CPCs from the T&E are connected to the cutouts MET. A single 6mm Earth going away from MET to bond water supply. All extraneous parts inside bonded in 6mm.

House DB made up of 2x 2kw convectors, 8.5kw shower, 5.5kw free standing cooker, 2x32A ring mains,1x Immersion heater. Storage HTG DB has 1x2.8 kW. All RCD protected.

Is the 16mm TE undersized to take load of House DB?

Table 4D5 suggests CCC using method 101 is 57A for 16mm TE. So, am I correct in giving this a Code 2? Even though this is original wiring when house was built (1 up 1 down) and there are no signs of thermal damage at either ends...

Is the DNO 100A main fuse sufficient protection for the 16mm TE?

I need to get my wording spot on as the Landlord is a retired spark!

Input please. Thanks
 
Hi,

scenario is. TNC-S 100A BS1361 main fuse at DNO cutout. 16mm tails feeding meter. 2x 16mm T&E cables coming out of meter (no switch fuse) going through wall (un-protected) up cavity across attic to the House DB and storage heating DB-both 15m away. Ze-0.17 pfc-1.32

The 6mm CPCs from the T&E are connected to the cutouts MET. A single 6mm Earth going away from MET to bond water supply. All extraneous parts inside bonded in 6mm.

House DB made up of 2x 2kw convectors, 8.5kw shower, 5.5kw free standing cooker, 2x32A ring mains,1x Immersion heater. Storage HTG DB has 1x2.8 kW. All RCD protected.

Is the 16mm TE undersized to take load of House DB?

Table 4D5 suggests CCC using method 101 is 57A for 16mm TE. So, am I correct in giving this a Code 2? Even though this is original wiring when house was built (1 up 1 down) and there are no signs of thermal damage at either ends...

Is the DNO 100A main fuse sufficient protection for the 16mm TE?

I need to get my wording spot on as the Landlord is a retired spark!

Input please. Thanks
Any Gas bond?
 
It says it on fuse carrier- I know could well be 60/80A but if it says it on the tin...

TE condcutors are in sleeving in their retrospective colours.
 
Those conductors can never be sleeved so they are suitably enclosed, nor will it provide adequate mechanical protection. You cannot predict what the fuse is in that carrier, given the distance they travel and their means of connection what is your view.
 
So, are you saying that when reporting the condition of an installation you would put the supply protective device characteristics as as Limitation even though the fuse carrier is labelled?

My view - cable is undersized.
 
I always state it is Not Verified. Whatever the fuse size it should be provided with circuit protection which in turn would enable correct connection of the cables.
 
You don't know the cable is undersized, I would say it has not been provided with suitable circuit protection. I would also say conductors are not suitably enclosed at the meter.
 
Lots of fuse carriers rated to 100A have 60A fuses round my way, I'm told. Just to add to the list, since its TNCS then Table 54.8 applies for the bonding conductor and 10mm is min.
 

Reply to EICR 1 bed flat- simples in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
802
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
I’m a trainee electrician and would really appreciate the benefit of someone’s skill and experience on the following: Our house is a TN-C-S (100A...
Replies
70
Views
6K
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board...
Replies
4
Views
1K
Came across this on an EICR and was wondering how everyone else would code it. Basically there’s a sangamo time clock that controls a contactor...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock