Discuss Superdeal Meter: how do they work & best way to connect Solar & Battery storage in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board for the house, (ii) DB2 - a small board for all storage heaters and (iii) DB3 - an even smaller board for electric water heating. Very high electricity costs which is why the client is exploring battery storage and solar. Ordinarily I would recommend a single Hybrid Inverter with DC Coupled battery storage and the Inverter wired via suitable RCD protection (with an AC Isolator in-between) to the main DB which feeds all the circuits in the house. In this case however, if connected to DB1, that would mean that the batteries, when charging from the grid, would do so at the day tariff rather than the lower night tariff. I don't know how the Superdeal Meter works so here's my daft questions: Q1. Are all the circuits connected to DB2 (currently storage heaters) able to draw power 24 hours a day so in effect - is the meter just monitoring power consumed during a night time window to apply the lower tariff ? Q2. Are alI 4 of the Lines (1 from the 100A fuse, the other 3 to DB1, 2 & 3) in the meter connected to the same physical bus bar ? If the answer to Q1 is Yes then I could alternatively connect the Inverter to DB2 (I would have to upgrade it latest regs) and configure the batteries to charge during the night at the low tariff. If the answer to Q2 is also Yes then during sunny days the generated power would flow through DB2 and become available to DB1 and DB3 to reduce how much they draw from the grid. Its possible that the meters reading consumption for DB1/2/3 could go negative on occasion. Even if the superdeal tariff goes away and/or gets replaced with an Econmy 7, similar priciples could apply. I'd be interested to hear other views / ideas and whether anybody else has designed something similar for this kind of setup. Thank you.
 
A picture of the meter and service head would be usefull
 
I have a client on a Superdeal tariff from SSE, the Superdeal Meter has 3 sets of tails coming out of it feeding 3 DBs: (i) DB1 - the main board for the house, (ii) DB2 - a small board for all storage heaters and (iii) DB3 - an even smaller board for electric water heating. Very high electricity costs which is why the client is exploring battery storage and solar. Ordinarily I would recommend a single Hybrid Inverter with DC Coupled battery storage and the Inverter wired via suitable RCD protection (with an AC Isolator in-between) to the main DB which feeds all the circuits in the house. In this case however, if connected to DB1, that would mean that the batteries, when charging from the grid, would do so at the day tariff rather than the lower night tariff. I don't know how the Superdeal Meter works so here's my daft questions: Q1. Are all the circuits connected to DB2 (currently storage heaters) able to draw power 24 hours a day so in effect - is the meter just monitoring power consumed during a night time window to apply the lower tariff ? Q2. Are alI 4 of the Lines (1 from the 100A fuse, the other 3 to DB1, 2 & 3) in the meter connected to the same physical bus bar ? If the answer to Q1 is Yes then I could alternatively connect the Inverter to DB2 (I would have to upgrade it latest regs) and configure the batteries to charge during the night at the low tariff. If the answer to Q2 is also Yes then during sunny days the generated power would flow through DB2 and become available to DB1 and DB3 to reduce how much they draw from the grid. Its possible that the meters reading consumption for DB1/2/3 could go negative on occasion. Even if the superdeal tariff goes away and/or gets replaced with an Econmy 7, similar priciples could apply. I'd be interested to hear other views / ideas and whether anybody else has designed something similar for this kind of setup. Thank you.
I think that was wishful thinking! If the attached image is correct for the Superdeal meter then the answer is No and Yes but given DB2 and DB3 are switched off by a timer, the only option is to connect the Inverter to DB1. There would be no way to charge the batteries from the low night tariff. A solar diverter for one of the Immersion heater feeds connected to DB1 could also help reduce energy costs during spring and summer.
 

Attachments

  • Supedeal Meter wiring.jpg
    154.9 KB · Views: 15
I think that was wishful thinking! If the attached image is correct for the Superdeal meter then the answer is No and Yes but given DB2 and DB3 are switched off by a timer, the only option is to connect the Inverter to DB1. There would be no way to charge the batteries from the low night tariff. A solar diverter for one of the Immersion heater feeds connected to DB1 could also help reduce energy costs during spring and summer.
Here's the meter:
 

Attachments

  • Superdeal meter.jpg
    238.4 KB · Views: 15

Reply to Superdeal Meter: how do they work & best way to connect Solar & Battery storage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
Hi all. We have had 7x 400w solar panels for a number of years now on our roof which is se/nw facing end terrace. 4 on se side 3 on nw side...
Replies
0
Views
821
I currently have a 3Kwh solar PV system which was installed over 12 years ago and getting a very good FIT payment and I don't want to lose it! I'm...
Replies
0
Views
4K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
552
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock