Hi everyone,
Looking for honest opinions on C2 ratings on a recent EICR. Terrace house probably built 1930's, rented out. Not sure if this is a standard EICR template but text and C2 ratings for the following:
1. Consumer unit - manual operation of circuit breakers and RCD's to prove disconnection (643.10)
2. Presence of RCD six-monthly test noticeat or near consumer unit (514.12.2)
3. RCD(s) provided for fault protection - includes RCBOs (411.4.204, 411.5.2, 531.2)
4. RCD(s) provided for additional protection/requirements - includes RCBOs (411.3.3, 415.1)
5. Provision of additional requirements for protection by RCD not exceeding 30 mA
- for all socket outlets of rating 32A or less unless an exception is permitted (411.3.3)
- final circuits supplying luminaires within domestic (household) premises (411.3.4)
Overall comments are:
No visible earthing on living room lighting circuit (C2/FI)
Property currently has x 2 consumer units with no RCD protection (C2).

I've been reading around the subject and on this forum and these things seem to be open to interpretation. If the work needs done, I have no problem with that, just don't want to be ripped off for work that's not actually required!
Would be grateful for comments.

Thanks
 
It is clear that RCD is an issue regards C2 or C3. Best practice Guide number four found on electricalsafety.org will say it is a C3, whereas codebreakers published by NAPIT call it a C2. Personally I usually put it as a C3 with certain caveats. i.e. if the installation is poorly executed and the residents not very aware of the potential dangers with electricity then it may be a C2. NAPIT say C3 because they feel tenants are an unknown and mixed lot and there is no telling how they may modify or change the layout of a place. Whether it is students having wild parties and trashing the house or a staid older working couple can be very different scenarios. As to no cpc on the lighting that again is easily C3 with a warning notice on the consumer unit not to put metal fitting or switches on the lighting circuits. It is not ideal but certainly can comply without the work needed dependant on the circumstances. I feel you should have been better informed as to the observations and it is a fine line in a stricter interpretation and breaching trading standards in recommending work that does not strictly need doing.
 
Last edited:
RCDs for faultprotection would be a N/A as long as EFLI readings were within limits for ADS.
 
RCDs for faultprotection would be a N/A as long as EFLI readings were within limits for ADS.
Annoys the hell out of me this one, it raises suspicions straight away that the report writer doesn't know the difference between RCDs for fault protection and additional protection!!!

In which case not only shouldn't be doing inspections, but shouldn't be let anywhere near this elastic-trickery stuff!
 
Thanks folks for your comments so far. As suggested on the thread earlier I have uploaded a copy of the report and would be grateful for opinions ?
 

Attachments

  • F743F98B-B7EB-42E5-8751-42B77ADFDE42.jpeg
    609.3 KB · Views: 50
  • 83C1152F-AA1F-436A-8208-657736E32702.jpeg
    550.1 KB · Views: 45
  • F5305591-4199-4592-A483-A59C52AF6038.jpeg
    569.1 KB · Views: 41
  • 140887C8-6461-489E-A34E-013BD35FF521.jpeg
    577.9 KB · Views: 41
  • 9B6A104F-0E16-4150-9F05-083F19718184.jpeg
    581.1 KB · Views: 47
  • FB44A34F-1F0C-4910-AB91-7AFB51FC1AA5.jpeg
    646.3 KB · Views: 50
We could spend a while picking holes here as there are a few nonsensical things in it.
I particularly note that he's apparently managed to do an insulation resistance test to earth on a lighting circuit that doesn't have an earth. That makes me wonder if any IR testing at all actually happened to check the wiring is in good condition.

With caveat that I haven't seen it for myself, two summary's coming up - what Best Practise Guide 4 says, followed by my real opinion!

So trying to look at it purely from a safety point of view in line with Best Practise Guide 4 says without personal preferences coming into it....
It looks like it met the regs when installed, it says there is supplementary bonding in the bathroom so the shower is ok.
If there are any sockets that could be used to serve equipment outdoors then there is a safety issue.
The lighting circuit is a safety issue if you have any metal fittings or switches.
With these caveats and not having seen it, it might just about scrape a satisfactory report.

My actual opinion.....
The wiring is likely 50 years old old if there is a lighting circuit without an earth.
I'm not confident the most important test to assess it's condition (insulation resistance) was actually performed. This is a very important test for older wiring.
The consumer units are doing their job but are mainly designed to protect the wiring not people. There are countless benefits to more modern consumer units as they offer a lot more to protect people.
If it were my house I'd want a trustworthy sparks to test the insulation, change the consumer units, and at a minimum rewire the lighting circuit.
If I was renting it out I'd also want tenants to be able to turn a breaker on not have to fiddle with fuse wire, and to be better protected by a modern consumer unit.

I hope that helps a bit.
 
I particularly note that he's apparently managed to do an insulation resistance test to earth on a lighting circuit that doesn't have an earth.
Whilst I fully agree with everything else in your post, I feel it proper to point out that there doesn't have to be a CPC present in order to do an insulation resistance test. The test will still show up insulation faults where the cables run next to earthed metalwork etc. And of course any line to neutral insulation leakage.
 

Reply to EICR - C2 OR C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I’m interested to hear other views on BS3871 MCBs being changed following a C2 non compliance on an EICR for over rated protective device. Eg...
Replies
9
Views
492
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
589
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock