I need a hand to confirm what coding goes with what please on this house
I have been asked to inspect a house by an agent and this is the situation:
Rewire was done about 1 year ago in old (Red & Black) cables, not notified, no certificate - landlord said the electrician and gas fitter walked off site due to payment problems (not a clue)
Boiler is less than 1 year old - never been serviced or when it was installed
I know a few of these are not a cause for concern but they are there to draw the picture
Thanks for your help
I have been asked to inspect a house by an agent and this is the situation:
- TN-S Earthing (0.4 ohms)
- No CPC in lighting circuit with Class 1 fittings
- No Bonding to Gas or Water
- No Sleaving on any CPCs
- All CPCs twisted together and put into 1 conductor on MET (in CU)
- Main Earth has been extended using a 6mm black (neutral) cable
- 10 Sockets on a 20A Radial (2.5 T&E)
- CU inaccessible under Stairs
- RCD as main switch (only 5 circuits)
- Trunking Missing exposing unsupported Cables
- Extractor Fan in bathroom controlled by the shower circuit (no shower) on 6mm T&E 32A MCB
- No labels on CU apart from an old damaged RCD label (this circuit or part of it is protected by an RCD)
- Half a socket in the kitchen does not work (245v LE, 110v LN, 110v NE)