Discuss EICR fail: No RCD Protection for lights etc. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Pthomsk1

DIY
Reaction score
0
I am a landlord and my managing estate agent just recently organised an electrician to carry out EICR. Came back as unsatisfactory, no RCD protection on: lights, smoke alarm, door bell and immersion heater. There is RCD protection on sockets and cooker. Electrician suggests changing the board. Is there an alternative eg. Adding another RCD to the current board? I was also worried that putting in a new board could cause other faults in the house that would then need remedying. House is mid 1990s construction.
 

Attachments

  • 906DC9E7-38B7-4FD1-BBF2-463BD711CB38.png
    902.9 KB · Views: 53
  • D8EFA797-C33E-4C37-9B86-5AACBC9F6A2D.png
    1.2 MB · Views: 52
A picture of your consumer unit and EICR with personal details redacted would help?

Also a CU change would not "cause" faults but simply highlight existing faults an old CU might not

You might think it is OK to leave faults in an electrical installation as long as you don't know about them because you are then forced to get them fixed which is very irresponsible and you are just leaving faults only to be discovered by your tenants which could have disastrous consequences

It is fixing these faults which could easily save someones life and it is your responsibility as a landlord to ensure your installation is safe which is the idea of an EICR
 
Check the report for other C1 or C2 codes.

Having no rcd on those circuits wouldn’t normally merit an unsatisfactory report but would simply be a C3: improvement recommended.

Although the electrician may code on the strict side as it’s a rental property.
 
Check the report for other C1 or C2 codes.

Having no rcd on those circuits wouldn’t normally merit an unsatisfactory report but would simply be a C3: improvement recommended.

Although the electrician may code on the strict side as it’s a rental property.
Agree thinking C2 for cabling in walls not Rcd protection that’s the Code Breakers code though… C3?
 
A picture of your consumer unit and EICR with personal details redacted would help?

Also a CU change would not "cause" faults but simply highlight existing faults an old CU might not

You might think it is OK to leave faults in an electrical installation as long as you don't know about them because you are then forced to get them fixed which is very irresponsible and you are just leaving faults only to be discovered by your tenants which could have disastrous consequences

It is fixing these faults which could easily save someones life and it is your responsibility as a landlord to ensure your installation is safe which is the idea of an EICR
I’ve added the photo of the consumer unit and summary of fails.
 
Looking at the observations....
If the existing RCD doesn't work, then I'd say that's a valid C2.
If the complaint is that all the circuits on the right have no RCD protection, then most people would judge that to be a C3 issue.

I'd suggest downloading the (free) best practise guide 4, read page 14, and ask the person who carried out the report whether there are good reasons the advice in BPG4 isn't being followed.


My informal opinion would be that there are some benefits of a board change (having lighting RCD protected so people changing bulbs have a little extra protection, having more modern Type A RCD technology, faults only taking out a single circuit, adding surge protection) but that is not the same as saying that it is potentially dangerous for the current installation to remain in service.

Can you clarify which are coded as C2 as it appears to be off the photograph.
 
Last edited:
Looking at the observations....
If the existing RCD doesn't work, then I'd say that's a valid C2.
If the complaint is that all the circuits on the right have no RCD protection, then most people would judge that to be a C3 issue.

I'd suggest downloading the (free) best practise guide 4, read page 14, and ask the person who carried out the report whether there are good reasons the advice in BPG4 isn't being followed.


My informal opinion would be that there are some benefits of a board change (having lighting RCD protected so people changing bulbs have a little extra protection, having more modern Type A RCD technology, faults only taking out a single circuit, adding surge protection) but that is not the same as saying that it is potentially dangerous for the current installation to remain in service.

Can you clarify which are coded as C2 as it appears to be off the photograph.
Hi Tim, the C2s I got we’re for all the red circuits that weren’t RCD protected. There’s no more information than is on the summary page other than in the relevant section it says c2
 
1673617172039.png
I've chopped off information that would identify the company and contractor.

I'm afraid there are some concerns about that schedule of test results.
There is certainly nothing on there to say the RCD works, there is no test data recorded for the RCD at all, not even that the test button works.
My top concern - there are some circuits that apparently had no R1+R2, R2 or Zs test which means there is no way of knowing that the protective device will trip under fault conditions, which is rather a fundamental aspect of testing.
My other big concern - if we believe the figures, there is one sockets circuit that has VERY low insulation resistance suggesting poor condition or damaged wiring and that would have raised concerns for me, and I'd have given that a C2.

One of two things happened. He either did an incomplete and in my opinion not very competent job, or he found enough things wrong to make it rather pointless continuing testing and stopped short.

Personally I wouldn't proceed with any recommended remedial work based on such incomplete test data.

Would you mind sharing your approximate location? There may be members nearby who can help resolve this.
 
My other big concern - if we believe the figures, there is one sockets circuit that has VERY low insulation resistance suggesting poor condition or damaged wiring and that would have raised concerns for me, and I'd have given that a C2.
If that really is the wiring then very worrying, but it could be the result of something like a surge-protecting extension block still being plugged in somewhere to that set of sockets. Or maybe a boiler with built-in SPD on a FCU somewhere, etc.

The lack of other info like RCD trip times, or R1+R2 on any other circuit, is not encouraging.
 
There’s another current thread that mentions with EICRs, if it complied at the time it was put in, but not now, it’s a C3….. if it never complied, then it’s the C1, C2….

Although it is down to the person doing the test at the time, and being rental, he may aim to get things changed to be safe as possible.

The faulty RCDs would of course bring a C2. Potentially dangerous. If there is a serious fault, the rcd may not trip, resulting in injury.
 
Although it is down to the person doing the test at the time, and being rental, he may aim to get things changed to be safe as possible.
The thing is, it should be about electrical safety for continue use, not personal preferences about installing the latest gear.
The faulty RCDs would of course bring a C2. Potentially dangerous. If there is a serious fault, the rcd may not trip, resulting in injury.
I'm with you there. The main thing this one swings on is whether that RCD works.
I'm thinking it likely that he started with sockets, then found the RCD issue. I'd have personally tested the rest anyway, as there are parts readily available for that board.
 
View attachment 105289
I've chopped off information that would identify the company and contractor.

I'm afraid there are some concerns about that schedule of test results.
There is certainly nothing on there to say the RCD works, there is no test data recorded for the RCD at all, not even that the test button works.
My top concern - there are some circuits that apparently had no R1+R2, R2 or Zs test which means there is no way of knowing that the protective device will trip under fault conditions, which is rather a fundamental aspect of testing.
My other big concern - if we believe the figures, there is one sockets circuit that has VERY low insulation resistance suggesting poor condition or damaged wiring and that would have raised concerns for me, and I'd have given that a C2.

One of two things happened. He either did an incomplete and in my opinion not very competent job, or he found enough things wrong to make it rather pointless continuing testing and stopped short.

Personally I wouldn't proceed with any recommended remedial work based on such incomplete test data.

Would you mind sharing your approximate location? There may be members nearby who can help resolve this.
Cardiff
 
In what reality is most of that NA?? Meaningless test result sheet.
Observation sheet says RCD faulty, without any indication of why, but if it is, then that's a C2, which could conceivably expand into a board change if a suitable replacement is unavailable.
 
In what reality is most of that NA?? Meaningless test result sheet.
Observation sheet says RCD faulty, without any indication of why, but if it is, then that's a C2, which could conceivably expand into a board change if a suitable replacement is unavailable.
I think the faulty part is that RCD protection does not exist for light, immersion, smoke alarm, doorbell. Might be wrong.
 
In that case the observation sheet is as ridiculous as the test results sheet.
Time to have a word with your agent, if that's the standard of testing their electrician produces.
 
In that case the observation sheet is as ridiculous as the test results sheet.
Time to have a word with your agent, if that's the standard of testing their electrician produces.
Can you walk away from an unsatisfactory EICR if you are unhappy with its standard and start again with a different electrician. Or are you duty bound to close out the fails on first electricians test sheet.
 
Both socket circuits appear to have been IR tested at 500V DC. To do that, you have to be quite sure there is nothing still connected. The one with the low IR value is typical of something still connected, I noted above mention of things like an extension block, boiler, some other FCU. Testing at 500V DC (if that was actually done) rather than 250V DC risks having blown whatever was still connected up.
 
There's no restriction on how often you can test an installation, and the one with the most recent date is the valid one.
So if I get another electrician who goes in and finds that those RCD issues (ie no RCD cover for lights, immersion, doorbell, smoke alarm) is c3 then I don’t need to close the c2s out from the previous report. Notwithstanding I guess that he may find issues that first guy hasn’t found. What qualification should I ensure someone who carries out an EICR has?
 
I think the guy who did the report is on about replacing current board with rcbo so maybe I just bite the bullet to future proof it eg. Maybe need electric car charging in future.
 
This one is tricky. Options are
a) Start again with different sparks, but have a discussion in advance about the previous report. When the other circuits are actually tested other issues may come to light of course. Provided the RCD works this could leave no remedial work being required.
b) Find another sparks to do the remedial work to address the issues (see below)
c) Accept the quote from the same sparks.

IF it emerges the RCD is broken, a replacement isn't exactly cheap (> £100 ) so replacing the board might in fact make more sense long term.
I may be doing the guy a dis-service but that report doesn't fill me with confidence. The idea is any sparks can understand what is wrong and provide a solution for fixing it. If it were me I'd feel I had to re-test things before I started coming up with solutions.
 
So if I get another electrician who goes in and finds that those RCD issues (ie no RCD cover for lights, immersion, doorbell, smoke alarm) is c3 then I don’t need to close the c2s out from the previous report. Notwithstanding I guess that he may find issues that first guy hasn’t found. What qualification should I ensure someone who carries out an EICR has?
The only real qualification needed is to be electrically competent and (of course) insured to carry out such work. However, EICR work needs more hands-on experience than many newly qualified sparks might think as it often deals with old or unusual systems that depart from what might be installed now.

I would suggest checking first if anyone on this forum is local and able to offer you their services. A proper inspection is not usually cheap as it is typically half to a whole day to do a decent job on most domestic size setup but an honest person is going to report what is really needed and not to do it superficially at a discount in the hope of making work for themselves.

If it is original 1990s equipment and you have plans for anything added in the future a new board might be a good plan is it is quite possible matching parts are no longer available. In addition you would have greater fault tolerance so if something does go wrong it is limited to a single circuit, etc. But get someone you trust first.

A failed RCD definitely needs fixing. The C2/C3 on missing RCD protection argument often comes down to the details (e.g. if for sockets could be used for outdoor tools like lawn-mower, or bathroom circuits, etc) and the spark's own judgment as to risk involved, but if getting it done then better to get it done properly and have no issues for a decade or more.
 

Reply to EICR fail: No RCD Protection for lights etc. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
598
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
596
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi all, have just ordered my first EICR ever for a studio to 1-bed conversion flat in London. It cost a little less than £80 and the electrician...
Replies
51
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock