Discuss EICR Help required from some of you testing experts. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
Please help, I'm still new to testing for myself and sometimes I wonder if my new Megger is being naughty on purpose as my Fluke wasn't as prone to throwing up weird results as my Megger.

So a mate has been doing very small works on a property and as he's there he finds pd's tripping on other circuits and strange faults so got a bit of a wobble and asked me to go do an eicr on the premises so agreed 50% sample with the owner.

I have had a good few hours on site today and not gotten very far due to the state the board was in, lack of correct labelling and so on...

Advice I'm looking for is I found a 2 gang dimmer hanging off wall which subsequently found is fed from a 32A ring and through a fused spur at 13A before ending feeding the said switch ! One dimmer is switching a load of LED downlights inside, other is a dummy dimmer / ordinary push on /off switch covering ground lights along outside wall which seem to be full of water droplets / condensation ! the suspected switch line to the out lights was discon in back of box, reconnected and switched all on, 10 seconds then bang and the back of the dummy dimmer was black as .... no 1362 fuse blown in spur and no rcbo tripped but switch was shafted cannot believe rcbo didn't trip ?? thinking must be shorted light fittings out there.

Next issue is on downstairs sockets, tests r1,rn, fine but r2 relationship 2.5/1.5 ratio is way off ! r1 0.44, rn 0.44, r2 16.8 kOhms !! wtf ?
Thinking nasty connection on cpc somewhere anyone seen similar before ripping apart the circuit.

R1+R2 was o.k. though.
IR was a real pain as the meter did not want to know: @500V L-E max was 1.01 Meg
N-E was 0.36 Meg !
But sure every single thing was unplugged.
Also when tested at 250V the readings all came out approx 25 Meg ! ??

What was even more weird was that entire board was off and locked off and every breaker or rcbo was open too. but while doing the downstairs sockets R1+R2 I tested the same at kitchen sockets which are a separate ring and they gave a result of 20+ K ohms ! surely the separate circuit should not have even registered ?

Following this the kitchen ring was tested and was o.k. until IR test again,
L-E max would go to was 30V
and L+N-E would not ramp up at all ! 0V
L-N also 0V would not ramp up at all.

Anyone ever seen any weird issues like these when trying to IR test or similar ?
I know the Megger will inhibit IR if it senses voltage above touch or a high resistance I think it was ? but is this likely or is my new MFT no good ?

Any ideas would help loads, Thanks.
 
think iwillpasson this one till the beer's worn off. toomuchinfofor a befuddled brain ( and that's when i'm sober)
 
Restrict the use of your all singing all dancing multi functional contraption for installations that are going to be straight forward
In the meantime get yourself a single instrument insulation resistance/continuity analogue meter,the system will then reveal its status more clearly than using a instrument that has too much influence on what and when it needs to function
 
Restrict the use of your all singing all dancing multi functional contraption for installations that are going to be straight forward
In the meantime get yourself a single instrument insulation resistance/continuity analogue meter,the system will then reveal its status more clearly than using a instrument that has too much influence on what and when it needs to function
like this:

upload_2018-3-14_22-39-6.jpeg
 
The poor dears these days wouldn't entertain the work involved turning the handle,it would never get up to speed and generate enough umph :)
 
Seems you have discovered why the external lighting was dissed. You are making the error of trying to find solutions to issues you are discovering instead of carrying out an EICR and itemising these issues in the Report. The problems with your meter is the reason I stick to individual meters and crack on with the job as opposed to fiddling with a temperamental meter.
 
So the question is - do you believe you results reflect the installation, or not? Is the kitchen ring IR result off because there is still something attached to it? I'd have another look perhaps then get on and record the result. Sounds like a few faults to be found later :) .
 
Restrict the use of your all singing all dancing multi functional contraption for installations that are going to be straight forward
In the meantime get yourself a single instrument insulation resistance/continuity analogue meter,the system will then reveal its status more clearly than using a instrument that has too much influence on what and when it needs to function

Been told this before and kindly even been lent a solo IR tester to check an install but still had the exact same issues ! so thinking it's probably not the test kit.
 
Best way to locate the high R2 on the ring is to connect only one cpc leg to the earth bar and test for Zs all round. With a continuity result in kOhms, you should see a massive rise in Zs value between two of the sockets, one of which will likely contain the loose connection
 
Thanks all so far, as I say I tried a solo IR tester before and it still wouldn't ramp up test jolts on a similar nightmare job. Did find a few stashed sockets with built in fridges in back of kitchen units etc.. but thought I had unplugged it all, no client home to check if more still hidden / connected ! Also owner did say 4 different electricians had worked on premises before over the years as so many different extensions / builders had done works and no certs or anything offered for works on electrics before !!
 
Best way to locate the high R2 on the ring is to connect only one cpc leg to the earth bar and test for Zs all round. With a continuity result in kOhms, you should see a massive rise in Zs value between two of the sockets, one of which will likely contain the loose connection
Thanks, never heard that one before. :thumbsup:
 
I'm old enough we had them at college years ago !

My apology if you thought that was meant for you,it was just old folks banter

Too many problems listed to comment on them all
Next issue is on downstairs sockets, tests r1,rn, fine but r2 relationship 2.5/1.5 ratio is way off ! r1 0.44, rn 0.44, r2 16.8 kOhms !! wtf ?
Thinking nasty connection on cpc somewhere anyone seen similar before ripping apart the circuit.

16,800 ohms will likely be open circuit rather than a nasty connection,that reading should be assessed in conjunction with the insulation resistance test on that circuit,it could be a reading of the cpc s of a open circuit with continuity via any appliances and associated copper pipes
 

Reply to EICR Help required from some of you testing experts. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
727

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock