Discuss EICR. Installation needs to meet 18th? in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 112675

Hello All

Planning on going away for a year or two and renting the house out so will need an EICR.

The consumer unit is old and has a 12 MCBs protecting each of 12 circuits. Some of the lighting radials are merged together under a single MCB. Suspect a 16 circuit cu might be better. Perhaps of more importance, there are no RCBs (and certainly no RCBOs).

From reading the forum it seems that perhaps some electricians would "pass" an EICR assuming it met the wiring regulations in force at the time of installation but some others would fail it unless it met the requirements of the 18th. The difference in cost is presumably quite large?

In any case, I'd probably quite like a new CU with RCD protection across all circuits. So I'm a bit torn: Do I spend a lot more cash and get a decent install or do I pay the minimum and get a certificate for what is already there?

The answer depends on ballpark cost. My total guess would be a new 16 way CU plus EICR would take one day whereas a cert might be done in an hour or so?

Have I got that right or am I totally wrong?

If I'm right am I looking at the difference between less than £100 and less than £1,000 ?
 
Hello All

Planning on going away for a year or two and renting the house out so will need an EICR.

The consumer unit is old and has a 12 MCBs protecting each of 12 circuits. Some of the lighting radials are merged together under a single MCB. Suspect a 16 circuit cu might be better. Perhaps of more importance, there are no RCBs (and certainly no RCBOs).

From reading the forum it seems that perhaps some electricians would "pass" an EICR assuming it met the wiring regulations in force at the time of installation but some others would fail it unless it met the requirements of the 18th. The difference in cost is presumably quite large?

In any case, I'd probably quite like a new CU with RCD protection across all circuits. So I'm a bit torn: Do I spend a lot more cash and get a decent install or do I pay the minimum and get a certificate for what is already there?

The answer depends on ballpark cost. My total guess would be a new 16 way CU plus EICR would take one day whereas a cert might be done in an hour or so?

Have I got that right or am I totally wrong?

If I'm right am I looking at the difference between less than £100 and less than £1,000 ?

An EICR on a 12 circuit CU should be best part of £200 or more depending on location. Why you believe a 16 way board will offer more safety or convenience I’m not sure. Nothing wrong with having more than one lighting radial terminated from a common MCB although not usually best practice, but you may have had new circuits added and the installer “tapped off” an existing circuit at the board. If you are letting and the installation does not have RCD protection to sockets and bathroom(s) then I’d advise you invest and upgrade - you will then know your CU, earthing, bonding, meter tails and all final circuits are safe and to latest regs. You will get an EIC and part P building completion certification that will cover you as part of the work. Expect to pay approx £400-500 for a dual RCD board or £600-£700 for an all RCBO board (Recommendation) assuming the installation had no faults and bonding and accessories are all wired ok
 
A proper EICR should take at minimum half a day to test all circuits and all points of the circuit.. These cheap EICR's have so many limitations they are not worth the paper they are written on. for 14 circuits your going to be looking at more like 250+ for an EICR. When you replace a consumer unit you need to do most of the tests for an EICR anyway so getting one done at the same time makes sense.

A replacement consumer unit with 14ways for a decent split load one with SPD and type A 100A RCD's to fit and install will be from around 500+ depending what extra work needs doing. Plus a bit more to do extra checks for EICR which may throw up other work that needs doing.

You don't need RCD protection necessarily (Depending on a few conditions) however as a landlord you have to think you need to be able to stand up in court and face the family when little Timmy does something stupid and is dead, if you get a cheap EICR with loads of limitations then was the installation safe, also you would need to live with yourself for the sake of 500+ is the cost you put on someones life.

Sorry to sound morbid but as a landlord you do have responsibilities.. Its entirely up to you but personally I would pony up and get a new consumer unit. With that many circuits and RCBO board will be way more expensive and although has its advantages for a board that size I dont think justifies the cost.
 
As above, an absolute minimum of half a day for 12 circuits, possibly a full day. Omission of RCD protection for ground floor socket outlets and possibly bathroom circuits will probably result in an unsatisfactory.
Combine an EICR with a CU replacement (with an EIC), RCD protection can then be installed to all circuits. As CU replacement requires full testing and inspection the cost of both as a combined job will probably be less than getting a properly carried out EICR and then needing a CU change anyway because of an unsatisfactory report. However it's quite possible that an EICR will identify other issues requiring rectification. An hour for a certificate? You have no idea how much work is required to do it properly.
 
Worth remembering, if you spend 1k on upgrading the board to a shiny new one with certificates to back it up, it is going to make any future house sale much easier and is probably worth the investment for that reason alone.

Not to mention improved safety as mentioned above.
 
Thanks for the replies. Quite useful and interesting.

It has influenced my decision which is to go for a CU change so glad I asked here.

Also interesting to read that some are making over a grand for a day's work in London.
 
Thanks for the replies. Quite useful and interesting.

It has influenced my decision which is to go for a CU change so glad I asked here.

Also interesting to read that some are making over a grand for a day's work in London.


A decent electrician is not "making over a grand a day". They're charging up to/about £1000. This includes materials, expenses and labour (which doesn't stop when they leave the job, there can be hours of paperwork to complete that is not seen). The ones pushing £1K plus in their sky rocket are most likely doing the reports and certificates from a quick visit, some photos, and the van.
 

Reply to EICR. Installation needs to meet 18th? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
787
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock